I have two project sites that have several CPU-319F-3 PN/DP PLC's installed on various material handling systems. In the last two months I have add errors on them were all of the status LED's on the PLC are flashing and there is message in the diagnostic buffer that reads[FONT=&quot] “DEFECTIVE: Internal System Error’ [/FONT] At one site it has happened to all five PLC's at the same time. This has happened twice in the last two month. On another site it has happened to two of the four PLC's but at different times. Here is a screen shot of the PLC version number. Has anyone else had an issue like this
Since it happens to several PLCs at the same time, it must be something external that causes it to happen.
Could it be caused by lightning strike ?
Is the earthing good enough ?
If the various PLCs are interconnected with each other, or other distributed panels or nodes, does everything have a proper equipotential earthing (not the same as common earth !).
Jesper, I am having my guys onsite check the grounding. On one site that is a distinct possibility as the electrical installation is not good. On the other site there was some lighting in the area at the time, but on the second occurrence I do not believe there was. Also on this site we have installed UPS's on the PLC's
Kalle, Yes they are all running the same version of firmware. So far Siemens has not been able to provide and real information on what might have caused it, other than a problem with the boot loader.
Hello, I have a CPU 317-2DP Firmware Version V2.1.8. In TIA Portal only V2.6 is available, and there is no option to upgrade FW. Then I open it...
Hey when I turn on my Siemens PLC CPU 216-2 after runing 10 minute it's stop and showing SF indication after I turn off and some time later turn...
140
I was trying to communicate between Siemens ET200S IM-151-8 PN/DP CPU to Rockwell Allen Bradley L73 through Hilscher Gateway NT100-RE-EN. Using...
119
I'll preface this by saying this is the first time I've worked on a Siemens system and I'm fairly unfamiliar with them. I might mess up some of...
29
798
Has anyone come across this kind of problem: I have 1215FC cpu with profinet and profibus devices. Because of one device, I would have to...
994