Hello
Generally, the order of EtherCAT slaves in my configuration matches how the slaves are physically connected.
Before I wade through a million settings, is it possible to give addresses to each slave, so I can happily expect to see them in any order?
I can certainly assign addresses, but thus far the physical order seems to be fixed.
Thank you
Pp
 
Hi, the last two times I used etherCat I had to address them in my tree to match the way they were hooked up. In a sense I could not connect them (like a star configuration) it seemed I had to connect them in a (linear ) fashion. What setting changed this I am curious.
Thanks.
 
Hello Bill
EtherCAT still requires the linear topology; you can't 'star' without using a branching unit, or also called an EtherCAT junction (it looks like a switch, but it's not a switch). They aren't transparent to the network, either. The need to be part of the configuration.

My Editor (Codesys V3) has a facility to write a specific EtherCAT address to the slave's eeprom. In my case though, one of the slaves had address rotary switches and these over-rode the eeprom setting.

Settings were as-you'd-expect after this. Let me know if you'd like any screenshots (if Codesys V3 is your thing)
Pp
 

Similar Topics

Hi, I am using vijeo designer v 4.6.. Now in my HMI program i was supposed to change a screen whenever user switches from Manual mode to Auto...
Replies
1
Views
1,800
Hoping someone can give me some guidance or confirmation of what I need to do. We have a FactoryTalk SE program that I need to change the IP...
Replies
2
Views
82
Hey all, i have a panelview screen (image attached), with 4 items on it. Program 1, Program 2, ...3, ...4. The PLC i am using is a compactlogix...
Replies
5
Views
169
Greetings I have a problem, my system is the following: wincc v8.0 (demo), logo8.3, abb m2m analyzer. I created some pages to display the...
Replies
0
Views
61
We had one go down. we have a new one. Their emergency Number don't work. The Model is TLSA046AAH-330N01-007 A catalog says we need software TET...
Replies
2
Views
170
Back
Top Bottom