Point IO IA4 module - where to find channel data?

selectionplc

Member
Join Date
Jan 2017
Location
Over there
Posts
9
I have a 1734-AENT configured in RSlogix 5000 with an IA4 module. I was expecting to see a controller tag something like FS1:1:I.Ch0Data, but I don't see any channel data anywhere. I just have FS1:1:I.0 - FS1:1:I.7.

Am I missing something or can somebody point me in the right direction? Thanks!

covpna


PointIOTags.PNG
 
Paully's5.0 said:
It's just a digital input module...

More specifically, the 1734-IA4 is a Point I/O four-point AC module. The "A" denotes the required supply voltage for the module. Not to be possibly confused with "A" denoting an Analog module.

That is if you are referring to "channel data" as being that of the Analog type? The example address "FS1:1:I.Ch0Data" would suggest as much?

Regards,
George
 
To add to George's reply an analog 4 channel module would be 1734-IE4C for current , or 1734-IE4V for voltage .
Regards,
Paul
 

Similar Topics

Good morning, I have a question regarding some point I/O modules. We use 1734-IE2V modules to measure the tension of a fiber, but we have quite a...
Replies
2
Views
72
Hi, I have some problem with View Point which I'm using to manual control of conveyors. On begin when in network was only PLC and HMI View Point...
Replies
0
Views
96
I have a bunch of tags in Historian/VantagePoint that off by one decimal point. I looked into the HMI displaying the same number, and the HMI is...
Replies
2
Views
135
Good morning, I have a Emerson/GE PLC with Cimplicity SCADA. I need to export data of a specific point/object to a CSV file and load the CSV file...
Replies
7
Views
324
Dear We are working in AB Studio 5000 and the drive is a PowerFlex 755T. For this project I need to control a conveyor to a certain set point...
Replies
2
Views
166
Back
Top Bottom