Is it possible to leave a "spare" terminal base for future use with 1794 Flex I/O? In other words
1794-AENTRXT
slot 0 - 1794-OE4XT
slot 1 - spare base for future use
slot 2 - 1794-IB16XT
I'm used to 1756 chassis with fixed slots.
this is my second message as my first was wrong....:sleep:
you use the bus connectors on the base, so the communications should be there.
Will you get a rack fault indication if there no module in slot 1?
Why can you not put a digital I/O module in there, leave it powered up, but no I/O involved? If you need to change it at a later date, then you can....
In the case as described, you can leave an empty slot in between modules and the diagnostics will simply show a module fault for the empty slot. The rest of the devices will function normally.
You can't put "reserved" slots to the right of occupied ones and configure your Studio 5000 I/O tree for the future devices, because the FLEX Adapter determines its "rack size" by examining the FlexBus at startup. The rightmost detected module determines the actual rack size, and it wouldn't match the configured size in the program.
Something i ran into that has me stumped, hopefully someone can explain. I have powerflex 70's connected to a L7 cpu using a 1788-en2dn. The...
1,357
Hi Everyone, Would like to ask about something we encountered on our work and would like some advise. We are upgrading a SLC controller to a...
2,469
Hey All, I'm currently building a control system for a large building in a industrial setting. Doing lighting, vent, roof control, door access...
3,498
I everyone someone can help me, I have a problem there's a fault in comunication, a controllogix lost conection with the RIo, RIO 0, RIO 1, RIO...
3,357
Hi Guys, I've been doing some experimenting in the shop and im hoping someone will be able to point me in the right direction. I was able to...
1,956