Siemens S7-1200 (CB1241 RS485) controlling Eaton inverter on Modbus RTU
aandjsam
Sep 2016
lincolnshire
30
Hi all,
I've hit a bit of a brick wall and need some help. I'm currently trying to get a Siemens S7-1200 PLC to talk to an Eaton DE1 Drive I'm using the CB 1241 RS485 Communication module, Wired like so:
M: Pin 1 (0V)
TA: Linked to T/RA
T/RA: Pin 7
T/RB: Pin 8
TB: Linked to T/RB
RTS:N/C
All I need is simple start and stop control with a speed reference, reading a fault from the drive would be handy if possible, also. This should be simple, but I just can't figure it out, I've only ever dealt with ethernet and profinet.
I've successfully loaded the MB_COM_LOAD FB and called it in the 'OB1' using the first scan bit. this loads without errors, I just can't figure out the MB_MASTER FB, what parameters need entering in it etc...
Hope you guys can help!
The DE1 Modbus RTU Manual:
ftp://ftp.moeller.net/DOCUMENTATION/AWB_MANUALS/MN040018_EN.pdf
TIA,
Sam
Thanks for those examples. What I'm wondering is why there is '40001' or '40002' etc.. being sent to the drive?
Modbus standards.
A 4 or a 3 and such will point to different locations such as "holding registers" "read single coil", "write single coil" and such.
Check out your Modbus mapping in the documentation for your device.
You should be able to find a description and the actual mapping in there.
Modbus standards.
That's fantastic, finally got a run signal going to it now! Thank you.
I have two MB_MASTER FB's, one for sending the run and another for sending the speed reference, the second one is generating an error code of 8080. Is there anything I may be doing wrong, I've got the second one being requested by the completion flag of the first one and latching with the 'busy' flag to hold the request until complete.
Just a quick update, I was using different instance data blocks, I'm now using the same for both MB_MASTER blocks and it now works perfectly.
Thanks a lot for your help!
Hi all, Currently having trouble getting a speed reference to write over modbus to an Omron M1... I can successfully write a run command and...
253
commentaire communiqué siemens s7-1200 avec vfd delta ? (cablage et sur tia portal )
129
Hi, I have a 1214 on ip 192.168.0.100. This is connected to other modules through a switch on same network. I need to connect this to a company...
179
Hi Experts, I would like to make firmware upgrade from v3.0 to v4.5 (S7-1200 CPU 1215C). Can I do it from v3.0 to v4.5? Do I need to take some...
287
Hi Guys, I am trying to establish communication over profinet between Siemens S7-1200 PLC as IO device and codesys plc as IO controller. But I am...
43
2,862