Shared AC bus on kinetix 5500 drives
piratedan200
Sep 2019
Ohio
I'm working on a project using a few kinetix 5500 drives, and I can't seem to get a straight answer from co-workers on power setup. I know you can use a shared AC bus, but AB literature states that you can only do so if the drives are the same (i.e. you can't put an H003 drive on the same power bus as an H008 drive). My co-workers said that it's not an issue and they've been doing it for years, so I'm trying to figure out if it's actually ok and just rockwell being overcautious or if there's a legitimate reason you shouldn't do it.
Do you mean a common DC bus but with each drive also receiving its own AC supply or do you mean no shared bus but a shared AC supply?
In the first case you want matched drives but in the second case it doesn't matter.
Does each drive have its own circuit protection or is that what you mean by "shared AC"?
Keith
That's what I thought, but per AB's literature:
What I've been told is that it's fine to share the AC bus and control bus on a single breaker without sharing the DC bus, but as you can see above, AB states you can only do that if the drives are all the same, hence my confusion.
I wonder if what they are stating is that to use the proper input protection fusing/breaker, in the single feeder/multiple drive configuration, the drives must be the same rating. Otherwise, the input protection would be too high or low.
I can only assume this applies to an application where only one drive is motoring at a time. If the DC bus were shared, 2 could be motoring while 1 was regenerating.
Hello all. Is it possible to create a shared folder between my laptop and my PV+ 7- standard......2711P-T10C21D8S Series D? What I would like to...
435
Hi All, i'm upgrading a [3x] GE 30-90 system that extensively uses %G Global Genius Tags via Genius bus. This is changing to RX3i (CPE310)...
568
Hello, is it possible to create a data block, something like shared datablock in Siemens STEP 7, in the RS Logix5000 PLC project? I would like...
1,065
Hello CODESYS experts, once again I need help. Trying to setup a PROFINET device which supports shared device function, has four (4) IO modules (2...
882
Greetings all, Wondering if produced consumed tags can be setup on a micro800 PLC? I'm trying to link 6 PLC's together so they have a few shared...
2,200