Need a little help
dalebartelds
Dec 2005
Byron Center, MI
I am just starting out with PLC programming and would like to ask for help. I have a machine that welds a clip onto a part that already has a nut on it. On this fixture I have a sensor looking for the nut to be on the part. Also I have another sensor to make sure the clip is in the fixture and lastly I have a sensor that makes sure there is only one clip under the part.
Right now if any of these sensors do not turn on the welder will not weld. The problem comes in when one of the sensors becomes shorted on all the time because of weld splatter. The operator will continue to weld parts sometimes without the clip being in place.
I want to use a PLC to make sure each of the three sensors turns on and off with each stroke of the weld cylinder. I've mounted a sensor on the cylinder so I am able to tell when it moves.
I have an Allen Bradley Pico to work with and I've read some of the tutorial. I sure would like a little help getting started.
Thanks,
Dale
well, a Pico isn't exactly a PLC...it's more of a smart relay. The Pico doesn't do sequencing, which sounds like what you need to complete your task.
Which type of Pico do you have, and do you have the software for it, or were you planning to program it from the face of the device?
A simple fault detector would be a timer for each of the three sensors. Start timing when the sensor goes ON and reset the timer when the sensor turns OFF. Select a preset for each timer based on how long each sensor should be ON in normal operation plus a little margin. If any timer's done bit comes on, that's an indication of a fault.
Besides monitoring the sensor for an always on condition, you should also be using a spatter and weld field resistant prox.
I presume that every time a part is placed in place and then removed after welding is complete.
I suggest checking all sensors to be ON before the welding cycle and then check for all sensors to be OFF when the part is removed after welding. This makes certain that the sensors are working properly.
I hope this helps.
Dale,
I uploaded the Pico software, and wrote you a little program. It was too big to display as a picture.
Thanks for the reply. I would like to use the 1760-L18 because I already have one. I know the software is a free download on the web and I think there is a laptop or two around with it already on it. But isn't it possibale to just use the screen to program it?
One of the problems is I only have enough room for a 5mm prox. I have not been able to find a weld splatter immune sensor that size. Balluff sells a ceramic face (604094) you can glue on the face of the prox that might help, I am trying that now but I still want to monitor the sensors.
Lancie1, Thanks for the drawing help. It gives me a good start. I'm not sure about the timers though. I think I would like to tie somthing into the stroke of the welder using the sensor I have on the cylinder. If I place the sensor half way up on the cylinder I should be able to see the cylinder as it goes up and then again when it comes down. I was just thinking maybe I need two sensors on the cylinder and then then I will know for sure where I am in the stroke.
Originally Posted by p.cooke
I am p.cooke. SEND me $1000 and i'll fix your problem. untill later
Sounds like a bargain! 'Specially after this post on another thread.
Well at least he is self assured and confident
Dan Bentler
I know you have counters in the Pico controller. If the Pico supports a compare instruction, setup a counter for each of the sensors. Compare the counter acc. If the values are different, one of the sensors is not reading correctly.
Hey guys, I have a client that has a v-notch chlorinator that doesn't run off a 4-20mA loop, it instead has two discrete inputs that drive the...
1,905
I was given a small PLC project from my dad for his company and I have ran into a few problems. I have found it necessary to use an output in my...
3,884
I am using a compactLogix PLC. We built a conveyor system now we have added an end of line sorter. Yes an add on and no one has thought of how it...
19
7,604
I need to use a contrologix 1100 to index a stepping motor. I will be using a IMS (intelligent motion systems) stepper driver and using the 1100...
1,186
Hello everyone, I want to know what I am doing wrong when trying to upload a program from a pv+1000 on a dh+ network. The 5/04 and HMI or talking...
1,456