1756-IF8 AI card drops current loop for a second

Troubleshooting an issue in which a 1756-IF8 AI card is usually working fine reading a ~12mA current loop from a device. When firing a relay from an adjacent relay output card, the current loop drops to 0 mA for about a second.

This seems to be caused by something in the IF8 card as the current loop does not change when bypassing the card/PLC. Got another card on order to test that theory, but does that problem sound familiar to anyone?

The IF8 card is configured as 8 single-ended 0-20mA inputs. Thanks for any info.

Last edited by MartyMaucher; January 8th, 2020 at 10:37 AM.
  Reply With Quote
Old January 8th, 2020, 12:20 PM   #2
GaryS
Member
United States

GaryS is offline
 
GaryS's Avatar
 
Join Date: Aug 2003
Location: Lancaster Pa.
Posts: 1,145
I would look at the loading when the relay pulls in
both cards may have a common power supply that is adequate.
  Reply With Quote
Old January 8th, 2020, 12:49 PM   #3
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 10,281
Quote:
Originally Posted by GaryS View Post
I would look at the loading when the relay pulls in
both cards may have a common power supply that is adequate.
If so, is there surge suppression on the relay coil?

I think it's always a good idea to have different power supplies for analog and digital input/outputs.
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Old January 8th, 2020, 01:00 PM   #4
GaryS
Member
United States

GaryS is offline
 
GaryS's Avatar
 
Join Date: Aug 2003
Location: Lancaster Pa.
Posts: 1,145
Quote:
Originally Posted by Mickey View Post
If so, is there surge suppression on the relay coil?

I think it's always a good idea to have different power supplies for analog and digital input/outputs.
if the power in pulled down with the coil energized a surge suppressor will not help they will only absorb the collapsing field surge when the coils is turned off

I fully agree that a separate poser supply for outputs is preferred for outputs
relays with a large load should have an Interpol relay to control them
  Reply With Quote
Old January 8th, 2020, 01:11 PM   #5
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 10,281
On second thought I should not have quoted your post. My comment was more about using the same power supply, if that is what the OP is doing.
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Old January 8th, 2020, 02:52 PM   #6
MartyMaucher
Member
United States

MartyMaucher is offline
 
Join Date: May 2014
Location: Pensacola
Posts: 90
Update: The device sending the 4-20mA signal is a new model ~$20K gas analyzer. After grounding the signal shielding wires, the current loop doesn't drop to 0 as often when activating the relay outputs (to valves).

I think the problem is in the device being sensitive to some electrical noise and it stops sending the signal for about a second and a half. One of those intermittent problems, but I'm leaning towards the PLC not being the cause.

I will look into more surge suppression on the relays, valves, etc. Thanks.
  Reply With Quote
Old January 8th, 2020, 03:29 PM   #7
GaryS
Member
United States

GaryS is offline
 
GaryS's Avatar
 
Join Date: Aug 2003
Location: Lancaster Pa.
Posts: 1,145
Make sure that you only ground the shield at one point only usually at the source.
if you use more then one ground point you create ground loop currents that can interfere with the signal.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
4-20 loop through NI8 card and DCS ??? karivelm LIVE PLC Questions And Answers 2 September 24th, 2008 08:51 PM
1756 Enet card and RSlinx ScottTheEngineer LIVE PLC Questions And Answers 5 July 17th, 2008 01:57 AM
High Speed AI card for Local vertual backplane in SoftLogix 5800 synclogix LIVE PLC Questions And Answers 0 August 8th, 2007 06:37 AM
1784-PCMK/B Card Health msinclair LIVE PLC Questions And Answers 6 August 13th, 2004 10:19 AM
1771-IT card equivalent in CLX (1756) ? grison LIVE PLC Questions And Answers 2 April 12th, 2004 12:55 AM


All times are GMT -5. The time now is 09:52 PM.


.