Analog input card 1756-IF8 not showing current inputs

MartyMaucher

Member
Join Date
May 2014
Location
Pensacola
Posts
91
I've got this 1756-IF8 card configured for 8 single ended inputs as shown below, but none of the channels are read real values (about 4 ma in the inputs, but showing -500). Is there something else to do after hitting Apply in the Configuration tab?
(I tried to upload a .zip of my .ACD project file, but it's too big).
- Logix Designer Studio 5000 v27.00
- 1756-L73 controller
- 1756-IF8 analog input

PLCAICard1.PNG PLCAICard2.PNG
 
Last edited:
Just a small note - in that screenshot, your PLC is in program mode (i.e. not executing code).

I would imagine that your I/O tables (including analog) would be updated even so, but I've never thought to check to be able to tell you that confidently. Someone else here may know.

Other than that, I'd be checking out Mickey's link. The value of -25 (assuming your input is scaled 4-20mA = 0-100, means that you're reading 0mA.
 

Similar Topics

Omron AD081-V1 Analog Input Card Offset & Gain Adjustment Entering Adjustment Mode 1. Set the input card in adjustment mode (Turn ON Dip SW No-1)...
Replies
0
Views
88
Good Morning , I have a RTD , that I would like to wire into a 1756-IF8 Analog Input Card. Would you all a simple wiring diagram , of what...
Replies
4
Views
1,203
Hello All, I am setting up a new RX3I test Rack with random I/O cards and a ( Horner ) HE693ADC420 analog input card. I do have a running system...
Replies
3
Views
1,670
Is it possible to wire a J type Thermocouple directly to a Allan Bradley Analog input card, specifically a 1769-IF4 card, and scale the reading to...
Replies
8
Views
2,544
Hello all. Is it possible to run an RTD to an Compactlogix Analog input module, without any sort of a signal conditioner or anything like that? Thanks
Replies
4
Views
2,212
Back
Top Bottom