1756-IF8 AI card drops current loop for a second
MartyMaucher
May 2014
Pensacola
91
Troubleshooting an issue in which a 1756-IF8 AI card is usually working fine reading a ~12mA current loop from a device. When firing a relay from an adjacent relay output card, the current loop drops to 0 mA for about a second.
This seems to be caused by something in the IF8 card as the current loop does not change when bypassing the card/PLC. Got another card on order to test that theory, but does that problem sound familiar to anyone?
The IF8 card is configured as 8 single-ended 0-20mA inputs. Thanks for any info.
I would look at the loading when the relay pulls in
both cards may have a common power supply that is adequate.
If so, is there surge suppression on the relay coil?
I think it's always a good idea to have different power supplies for analog and digital input/outputs.
if the power in pulled down with the coil energized a surge suppressor will not help they will only absorb the collapsing field surge when the coils is turned off
I fully agree that a separate poser supply for outputs is preferred for outputs
relays with a large load should have an Interpol relay to control them
On second thought I should not have quoted your post. My comment was more about using the same power supply, if that is what the OP is doing.
Update: The device sending the 4-20mA signal is a new model ~$20K gas analyzer. After grounding the signal shielding wires, the current loop doesn't drop to 0 as often when activating the relay outputs (to valves).
I think the problem is in the device being sensitive to some electrical noise and it stops sending the signal for about a second and a half. One of those intermittent problems, but I'm leaning towards the PLC not being the cause.
I will look into more surge suppression on the relays, valves, etc. Thanks.
Make sure that you only ground the shield at one point only usually at the source.
if you use more then one ground point you create ground loop currents that can interfere with the signal.
Good Morning , I have a RTD , that I would like to wire into a 1756-IF8 Analog Input Card. Would you all a simple wiring diagram , of what...
1,205
I am looking for information on the proper calibration of an 1756-IF8 analog input card, preferably the wiring of the voltage source. Rockwell...
8,053
I've got this 1756-IF8 card configured for 8 single ended inputs as shown below, but none of the channels are read real values (about 4 ma in the...
2,571
I've searched Allen Bradley and online, but cannot figure out how to configure this 1756-IF8 card to 8 single-ended analog inputs in the Logix...
3,431
Hello, Currently my IF8 is set as 1756-IF8/B Revision 2.011 and my PLC only register as 1.011 which I unable to get the data from the sensor...
1,456