There may be a little bit to configure. Just look back at my first post:
Under it should be listed five different HSC's. Enable one. When you enable it, the fields to set it up become active.
Scroll down til you see Function.
For Type of Counting, select Frequency.
For Frequency Measuring Period, select 1.0 Sec.
The other settings depend on your setup.
Go alittle further down and view the Start Address. It should be something like 1016, and is a double word.
When you enable the HSC I think the default for type of counting is COUNT, so you will have to select Frequency. that may be all you have to do.
Yes, just move the ID1000, or whatever address for the HSC you're using, into any other memory double word address and it should be OK.