S7-1200 ctrl hsc problem
Blue Fox
Feb 2013
Basildon
49
Hello all,
I have a strange problem with a high speed counter with a s7-1200. I have set up the hack input - it is a 2 channel a/b type which gives 500 pulses per revolution. I also put the ctrl_hsc, created the data blocks etc. For some reason if I read the return directly from the encoder without the ctrl_hsc enabled (put an N/O in front of it) the return reads correctly at 500 pulses per revolution, however if I do it with the ctrl_hsc enabled it only reads about 120 pulses per rpm? I can’t understand or figure out why this is. Is anyone able to offer any advice?
About 120, would that be 125 by any chance. In which case you are looking for a calculation that includes the quadrature function of the AB high speed input. 500 / 4 = 125. Does the program allow for the quadrature output and so divide the HSC output by four, if so you should set the HSC to 'A/B Counter fourfold'.
One other thing, when you read the value of the HSC use the P option to get the reading right now. So instead of reading ID1000 you use ID1000:p. From the manual 'Append the suffix ":p" to the I/O address if you want the program to immediately access I/O data directly from the physical point instead of using the process image.'
Just a quick update on this. I have replaced the ctrl_hsc with a ctrl_hsc_ext and this has solved the problem. It seems the ctrl_hsc is a “legacy instruction” so I think that may have been having issues with the v4.2 firmware. I ha e bench tested it at the workshop and it’s all working spot on now so going to site tomorrow to update on site plc and hoping all will be ok.
Hi all, Currently having trouble getting a speed reference to write over modbus to an Omron M1... I can successfully write a run command and...
255
HI i would like to know how to get a variable that will store the amount of times a program has been executed. The issue is I have 3 DBs for 1 FB...
82
Hi, I have attached herewith one image which our programmer has been used in S7 1500 PLC. Now we need to use the same instructions in S7 1200 PLC...
120
commentaire communiqué siemens s7-1200 avec vfd delta ? (cablage et sur tia portal )
132
Hi, I have a 1214 on ip 192.168.0.100. This is connected to other modules through a switch on same network. I need to connect this to a company...
181