Trouble Connecting Micro820 PLC to Fanuc Robot Controller
What are you trying to accomplish?
If all you want to do is have the PLC command the robot to perform some actions and to tell the PLC when it is performing those actions, the easiest approach is to hard wire PLC discrete outputs to robot discrete inputs and robot discrete outputs to PLC discrete inputs.
I already have a fanuc program set up that I would like to call, that I want use to start/stop/pause/etc via the HMI and PLC. I don't need to directly call inputs and outputs, rather just the ability to start and stop a program as well as other tags (fault, busy, etc) for indicators on the HMI.
Are you sure the Fanuc robot supports Ethernet IP?
Yes, I have the correct modules on the robot, it's a matter of understanding the CCW side that I'm having trouble with. I don't understand how to configure a PLC with an ethernet module. All I can do is change the IP address, subnet mask, and gateway.
The micro820 only supports 3 different "Ethernet/ip" protocols(as far as I know!)
1- CIP explicit
2- CIP symbolic
3 Modbus Tcp
So which one are you using?
1- CIP explicit
2- CIP symbolic
3 Modbus Tcp
I'm not entirely sure, actually. I just started using PLCs recently so I am not terribly proficient with the terminology yet. I thought I would be able to connect the PLC, HMI, and robot to a network switch and configure the robot so that I can see its tags in the PLC. I thought Ethernet/IP was its own communication protocol.
CIP Explicit is the way to go
I have realized that the Micro820 controller does not have the ability to configure generic ethernet modules (like the controllogix controllers) so it is not possible to connect as a scanner that way. You need to use CIP explicit messaging to communicate between a Micro820 and a fanuc robot.
Thanks for the advice though.
I have a new job programming PLCs and HMIs after being away from them for ~7 years. I am trying to establish a test setup with an old AB...
3,919
I have a problem connecting to a Controllogix L71 (version 20) via a 1756-EN2TR/C (Revision 10.0007). Secomea is a 3549 with the latest firmware...
1,676
Hello, I am very new to this new hobby and am having difficulties connecting to my PLC CPU. I am not sure if I am doing something completely...
18
5,191
Was wondering if anyone had any suggestions: I'm trying to connect to an old PanelView 1000 Touchscreen model# 2711-T10C16L1 via RS-232. I'm...
3,686
Good Afternoon, I'm currently trying to upload a program from an old GE 90-30 CPU with a Windows 10 laptop that is running Proficy Machine...
3,207