FactoryTalk View Studio HMI with Remote IO Scanner
I'm trying to develop a program in FactoryTalk View Studio 5.10 for a PanelView Plus 1500.
I set up the RIO driver in the Communications tab and created some aliases to use for the bits I want to read. But the RIO aliases are not coming up in the tag browser when I try to attach them to objects in my displays. I tried "Refresh Folder" and "Refresh All Folders" and nothing is coming up. What step did I miss? I can't find any how-to articles for a newer 5.x FactoryTalk, so the screens in the articles I'm looking at are a bit different. |
![]() |
![]() |
#2 |
Member
![]() ![]() Join Date: Feb 2012
Location: Chicago, IL
Posts: 24
|
Here are a few screen shots.
1 shows the RIO configuration in the communications tab, with aliases set up. 2 shows the tag browser in the Application, which isn't showing any of the aliases I set up for RIO communication. |
![]() |
![]() |
#3 |
Member
![]() ![]() Join Date: May 2003
Location:
Posts: 1,858
|
Did you setup your shortcut in the communications setup and point it to the controller?
__________________
There Is A Frost Advisory...GBR! |
![]() |
![]() |
#4 |
Member
![]() ![]() Join Date: Feb 2012
Location: Chicago, IL
Posts: 24
|
I'm looking at help files to try and figure out how to do that.
It tells me to click the + sign next to "RSLinx Enterprise" to select Communications Setup. There is no + sign there, like there are no sub-items under "RSLinx Enterprise" |
![]() |
![]() |
#5 |
Member
![]() ![]() Join Date: May 2003
Location:
Posts: 1,858
|
I see that. There is a thread on here some where about registering a .dll to fix an RSlinx Enterprise issue. I don't know if that will fix your issue or not.
KB 33825 talks about this issue but you need a support contract to view it and it talks about reg the .dll
__________________
There Is A Frost Advisory...GBR! Last edited by Bob O; February 8th, 2012 at 10:20 AM. |
![]() |
![]() |
#6 |
Member
![]() ![]() Join Date: May 2003
Location:
Posts: 1,858
|
__________________
There Is A Frost Advisory...GBR! |
![]() |
![]() |
#7 |
Member
![]() ![]() Join Date: Feb 2012
Location: Chicago, IL
Posts: 24
|
Yes! Re-registering the DLL files per this thread fixed the RSLinx issue, and I was able to create the shortcut.
http://www.plctalk.net/qanda/showpos...54&postcount=5 |
![]() |
![]() |
Bookmarks |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
FactoryTalk View Studio ME RSLinx Enterprise Shortcut Issue | DamianInRochester | LIVE PLC Questions And Answers | 16 | April 22nd, 2014 06:17 PM |
Factory Talk View Studio v5.1 to v5.0 Incompatability | bkfrodo | LIVE PLC Questions And Answers | 3 | October 2nd, 2011 09:59 AM |
FactoryTalk View Studio 6.1 SE Network Project, Display Component not Found Issue | tatsumasa | LIVE PLC Questions And Answers | 3 | September 2nd, 2011 06:54 PM |
PLC-5 Question for Online Addition of Flex IO AI card on Remote IO Link | usman379 | LIVE PLC Questions And Answers | 2 | December 28th, 2010 05:13 PM |
RS View Studio Is It Compatible With Factory Talk View? | randy741985 | LIVE PLC Questions And Answers | 8 | February 7th, 2010 11:55 AM |