Old December 11th, 2017, 12:32 PM   #1
stu
Member
England

stu is offline
 
stu's Avatar
 
Join Date: Aug 2005
Location: England
Posts: 588
Help with plc relay stuck on

Hi guys
I have an issue on a micrologix 1400 1766-L32BXB , this morning I had an issue with 2 outputs on the base unit stuck open (constant supply)
The two outputs in question enigize 2 relays R2 & R3 this then operates the run signal to 2 inverter?

I check out the wiring for feed back ? Which could cause emi to the plc - nothing wrong??

I changed the plc and after a hour R 2 coil signal was stuck open ??
I canít find anything wrong though?
Do you think I should put a diode across the relay so we donít get a surge back to the plc??
Thanks Stu
  Reply With Quote
Old December 11th, 2017, 12:48 PM   #2
scott.lawrence
Member
United States

scott.lawrence is offline
 
Join Date: Feb 2010
Location: Columbus, Ga
Posts: 81
are you using a suppressor on the relay itself?
  Reply With Quote
Old December 11th, 2017, 12:58 PM   #3
stu
Member
England

stu is offline
 
stu's Avatar
 
Join Date: Aug 2005
Location: England
Posts: 588
No there is nothing fitted on the relays ,this is an old install?
  Reply With Quote
Old December 11th, 2017, 01:17 PM   #4
James Mcquade
Member
United States

James Mcquade is offline
 
Join Date: Oct 2007
Location: Tennessee
Posts: 2,013
Your post is a confusing to me, so I will cover what I know.

your plc outputs are relay type powering interface relays going to inverter run inputs.

Plc
all relay type plc outputs have a lifespan, I do not know your plc outputs life.
if the outputs are dc, I would use a reverse diode to protect the relay.
if it's ac, I would use an ac suppressor.
if the outputs are high cycle, I would go with a triac output module and load resistors.

if the contacts have high current over a long time, the relay contact arm itself could be overheating and bending, breaking, or welding the contacts.

in regards to the plc outputs, how much is the inrush current to the interface relays? I would multiply the holding current by 6 to 10 for that.

for the relays R2 and R3.
the same applies as above.
I wouldn't think a contact closure to an inverter for the run signal would cause this issue in an hour. Please check the inverter's wiring diagram versus what is wired.

regards,
james
  Reply With Quote
Old December 11th, 2017, 01:21 PM   #5
GaryS
Member
United States

GaryS is offline
 
GaryS's Avatar
 
Join Date: Aug 2003
Location: Lancaster Pa.
Posts: 592
I agree the post is confusing to me to but
can you go online with the PLC ?
can you force the outputs on ?
when they are forced on do the close ?
what dons the program request them to do, the rung controlling the output all true ?
  Reply With Quote
Old December 11th, 2017, 01:42 PM   #6
stu
Member
England

stu is offline
 
stu's Avatar
 
Join Date: Aug 2005
Location: England
Posts: 588
Yeah I can go online and toggle the outputs which they come on and off but I have a constant 24vdc through the plc output (like the relay output has welded together)

And after the plc output we are connected to a relay - which is the inverter run signal ?
I’m thinking we need a reverse diode or a suppression,but not sure
  Reply With Quote
Old December 11th, 2017, 01:48 PM   #7
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 9,920
Quote:
Originally Posted by stu View Post
Yeah I can go online and toggle the outputs which they come on and off but I have a constant 24vdc through the plc output (like the relay output has welded together)
Which outputs are you connected to? Group 2 are solid state. (leakage)
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Old December 11th, 2017, 01:49 PM   #8
rupej
Member
United States

rupej is offline
 
Join Date: Sep 2014
Location: NC
Posts: 246
Which outputs on the PLC are staying on? The relay outputs or the transistor outputs? Are all your DC coms for the transistor outputs wired correctly?
  Reply With Quote
Old December 11th, 2017, 01:53 PM   #9
stu
Member
England

stu is offline
 
stu's Avatar
 
Join Date: Aug 2005
Location: England
Posts: 588
Now that's a thought I will check thanks
  Reply With Quote
Old December 11th, 2017, 02:01 PM   #10
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 9,449
That particular model of Micrologix has FET outputs for points 2 through 7 (Group 2). This type of output requires a DC common signal be wired to the terminal marked "COM 2" in order to work properly.

I learned about this detail the hard way myself. I had some stuff wired to the first four outputs. Outputs 0 and 1 worked fine, but outputs 2 and 3 seemed to leak too much to let my little interposing relays drop out when the signal was off. I moved them to the relay outputs at points 10 and 11 to get the machine running. Then I went into the manual and figured out where I went wrong.

With relay outputs and many with solid state outputs you only need to supply VDC to the right terminals, but with the micrologix FET outputs you also need DC common wired to all the right places.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
  Reply With Quote
Old December 11th, 2017, 02:13 PM   #11
stu
Member
England

stu is offline
 
stu's Avatar
 
Join Date: Aug 2005
Location: England
Posts: 588
Ok that’s interesting on the outputs we have 24vdc linked to the vac dc0, vacdc1, dc2, vacdc 3, vacdc 4 , vacdc5 ? Which has been wired up like this for a while ??
Is this right ??
  Reply With Quote
Old December 11th, 2017, 02:22 PM   #12
stu
Member
England

stu is offline
 
stu's Avatar
 
Join Date: Aug 2005
Location: England
Posts: 588
So the Fet group 2 outputs need the dc common 0vdc ??? Not 24vdc
  Reply With Quote
Old December 11th, 2017, 02:34 PM   #13
rupej
Member
United States

rupej is offline
 
Join Date: Sep 2014
Location: NC
Posts: 246
VDC2 needs 24VDC, and COM2 needs the common. Lots of people leave off the common and the outputs can do strange things, like "stick" on. Take a look and report back.
  Reply With Quote
Old December 11th, 2017, 02:36 PM   #14
stu
Member
England

stu is offline
 
stu's Avatar
 
Join Date: Aug 2005
Location: England
Posts: 588
Ok thanks
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
PLC vs relay interlocks g.mccormick LIVE PLC Questions And Answers 7 December 6th, 2015 08:43 AM
Im totally new! Please help! Tool changer PLC mike^3 LIVE PLC Questions And Answers 34 November 3rd, 2015 04:28 PM
PLC Update - Back Issues Collection Now Available! Phil Melore LIVE PLC Questions And Answers 11 October 22nd, 2015 02:17 AM
PLC 5 multiple outputs stuck high on multiple cards jschapansky LIVE PLC Questions And Answers 4 March 14th, 2009 10:22 AM
External Relay causes PLC fault triplewhammy LIVE PLC Questions And Answers 39 January 16th, 2007 10:30 PM


All times are GMT -5. The time now is 07:20 PM.


.