Hi,
Looking for some advice regarding the tag update setting in Panelview Plus 7 terminals. We’re starting to install these as upgrades from old DH485 PV550s.
We have several sites. But typically we might have a network with between 2 and 20 SLC 5/05 PLCs, each with a Panelview Plus 7 at each PLC. All the PLCs and HMIs are communicating via managed switch’s, and each HMI only has a shortcut to its own PLC. We also have iFix SCADA on the network. The PLCs all message each other, but they do so on a token basis within each PLC, so only one MSG instruction is executing in each PLC at a time.
The SCADA is set to poll the PLCs for tag updates every 5 seconds, with analogues polling every 1 second.
I think the panelviews poll at 0.25 second intervals.
My question really is, what is the effect of the 0.25 second update time? Will it start flooding the network with traffic? Or is it likely to cause no problems? Do they only update while the page is the current display? Or are the pages updating all the time in the background?
It’s making me think, why there are so many update time options. The SCADAS are apparently set to poll at 5 seconds so they don’t overload the network, but this might be an historical thing from the DH+ days.
On one site - since these panelviews have gone in, the comms times seems to have been causing a few issues - sometimes activating the watchdog timer alarms. But then someone’s been messing about with the SCADA as well - so that could be the issue
Any thoughts on update times on the Panelviews welcome....
Thanks
Andy
Looking for some advice regarding the tag update setting in Panelview Plus 7 terminals. We’re starting to install these as upgrades from old DH485 PV550s.
We have several sites. But typically we might have a network with between 2 and 20 SLC 5/05 PLCs, each with a Panelview Plus 7 at each PLC. All the PLCs and HMIs are communicating via managed switch’s, and each HMI only has a shortcut to its own PLC. We also have iFix SCADA on the network. The PLCs all message each other, but they do so on a token basis within each PLC, so only one MSG instruction is executing in each PLC at a time.
The SCADA is set to poll the PLCs for tag updates every 5 seconds, with analogues polling every 1 second.
I think the panelviews poll at 0.25 second intervals.
My question really is, what is the effect of the 0.25 second update time? Will it start flooding the network with traffic? Or is it likely to cause no problems? Do they only update while the page is the current display? Or are the pages updating all the time in the background?
It’s making me think, why there are so many update time options. The SCADAS are apparently set to poll at 5 seconds so they don’t overload the network, but this might be an historical thing from the DH+ days.
On one site - since these panelviews have gone in, the comms times seems to have been causing a few issues - sometimes activating the watchdog timer alarms. But then someone’s been messing about with the SCADA as well - so that could be the issue
Any thoughts on update times on the Panelviews welcome....
Thanks
Andy