ControlLogix talking to Schneider PACDrive LMC

sanger

Member
Join Date
Nov 2005
Location
Toronto
Posts
172
What is required for a ControlLogix PLC to read/write tags from a Schneider PACDrive LMC PLC? Does the PACDrive have Ethernet/IP protocol built in or is extra hardware required?
 
Which model PacDrive LMC? The LMC300/400/402/600/802 have the ability for EIP Scanner or Adapter built in. The LMC101/201 needs an option card added to the slot on the bottom.
 