ABCIP.5 lost connection some time with 1756-L71 5570 Controller Rev.21.11
jonney
Apr 2012
Malaysia
70
Environment:
MMI Side: Intouch 10, ABCIP.5 connects with one 1756-L71; ABTCP.1 connect with few PLC5 1785-40E
PLC side : 1756-L71 5570 Controller Rev.21.11, 1756-ENBT/A; PLC5: 1785-40E
Studio 5000 V21.00
Almost every half hour (random), I still see the Heart bit is still blinking on Intouch MMI, but the REAL/Float data are not updated. Some time,both Bits and Real data can't be updated.
I resolve the problem by Choosing "No optimization Mode" instead of default "Optimize for read". So far so good after the changes in 4 hours.
I read the ABCIP.5 manual, Page 111-112 is talking about the requirements . But on my side, the L5571 has firmware 21.11, so it does support "Optimized mode".
Anybody has similar case? Any more specific document can be refered for my problem?
Edited: PLC5 connections are always OK. I used ABTCP.1 connects to 3 PLC5 1785-40E.
oops, it stop updating the Intouch I/O REAL again even though the heart bit is blinking (bit data is updating but I/O Real data is not updating).
Now I clear the Intouch historical data and switch off the windows firewall to see any improvements.
Have you checked the resources on the ethernet card?
You can monitor some stuff on RSLinx like the attached pictures
The PLC has a max number of connections that can be active at once, across IO and programming. I don't expect that you have hit that. But you may have to manually increase your message buffers. We have not used Intouch for a few years so I don't know what they are using for their communications any more
The Ethernet card has limits as well, connections, buffers, and bandwidth. Which ethernet card are you using? 1756-ENBT. EN2T, etc. This would be where I would look first.
It's been a while since I have looked into this stuff. We spend a lot of effort making sure we don't exceed the communication limits on our ControlLogix
We used 1756-ENBT/A which has good configuration.
Intouch 10 only read and write total 8 I/O Real data from L5571.
I think the problem comes from the known issue. But I am not so sure because I don't have the hotfix L00137689. I am contacting Wonderware support.
Hola chicos. Tengo un problema con el driver de comucicacion dasabcip 5, y un plc controllogix v34, ya realice la comunicacion pero en ciertos...
173
Hi. I'm testing a few communication bits to monitor the communication health between InTouch 2023 and a L71 PLC. To do so, I disable OI.ABCIP...
570
Have a customer that has a running 1756-l83es, communicating to redundant ABCIP IO servers for Wonderware 2020. This configuration has been...
892
What's the fastest practical Update Interval you've had success with on the ABCIP driver communicating to L7x series Control Logix? Have an...
637
Having a Issue at a site where WOnderware can seemingly connect to the PLC and all shows good except its locked into a loop for downloading the...
1,822