OK to Tie Powersupply Common to Chasis Ground?

Wondering what are the pros/cons of tying Power +24VDC supply Common to chassis (earth) ground. Is it OK to do so? I have seen some control panels where this is done and others without. I have also seen Dual polarity supplies +/-15VDC commons tied to chassis ground as well. What determines if a power supply common should or shouldn't be tied to a chassis ground?

Thanks
  Reply With Quote
Old June 15th, 2017, 04:19 AM   #2
BobB
Lifetime Supporting Member
Australia

BobB is online now
 
BobB's Avatar
 
Join Date: Jun 2002
Location: Sydney
Posts: 4,194
Why? I never tie 24VDC or 24VAC to ground. That being said my 24VAC is always through a double wound transformer and 24VDC through a switchmode power supply - grounding the negative removes isolation. No pros - only a huge con - remove isolation. For example if the 24VDC negative is grounded there is a path to ground in the field - if not no path - no shorts - no blown up input cards.
__________________
The Old Pfhaart

  Reply With Quote
Old June 15th, 2017, 04:40 AM   #3
g.mccormick
Member
United States

g.mccormick is offline
 
Join Date: Jul 2012
Location: IN
Posts: 419
I almost always tie 24 vdc supplies to ground. Yes it removes isolation, but that can be safer if somehow a different voltage gets on it. Example would be 480 somehow vets tied to it. If not grounded then theoretically no circuit protection would open and an unsuspecting person could come into contact with 480AC. I've also seen it clear up noisy analog signals by tieing to ground.
  Reply With Quote
Old June 15th, 2017, 07:44 AM   #4
NetNathan
Lifetime Supporting Member
United States

NetNathan is offline
 
Join Date: Nov 2011
Location: Corona, CA
Posts: 1,267
Quote:
Originally Posted by g.mccormick View Post
I almost always tie 24 vdc supplies to ground. Yes it removes isolation, but that can be safer if somehow a different voltage gets on it. Example would be 480 somehow vets tied to it. If not grounded then theoretically no circuit protection would open and an unsuspecting person could come into contact with 480AC. I've also seen it clear up noisy analog signals by tieing to ground.

I have even had the analog out on some devices not work unless the 24VDC negative is grounded and yes also to noisy analog signals if not grounded.
__________________
****Control Freak****
Net is where I be and Nathan is me.

Last edited by NetNathan; June 15th, 2017 at 07:47 AM.
  Reply With Quote
Old June 15th, 2017, 09:41 AM   #5
BryanG
Member
United Kingdom

BryanG is offline
 
Join Date: Feb 2005
Location: Manchester
Posts: 1,138
Do a search here, you will find the subject has been covered many many many times, there are entrenched views on both sides. In my understanding one side is right and one side is wrong, but I am not telling which is which.
  Reply With Quote
Old June 15th, 2017, 10:28 AM   #6
AutoMax
Lifetime Supporting Member
United States

AutoMax is offline
 
AutoMax's Avatar
 
Join Date: Apr 2017
Location: Indiana
Posts: 217
I've seen it done both ways, and depending on which set of regulations you're working to it might be interpreted as mandatory. I've never personally solved a problem by grounding an ungrounded system, but I have solved problems by removing the ground.
  Reply With Quote
Old June 15th, 2017, 10:39 AM   #7
KuulKuum
Member
United States

KuulKuum is offline
 
Join Date: Jun 2006
Location: Texas
Posts: 122
Quote:
Originally Posted by AutoMax View Post
I've seen it done both ways, and depending on which set of regulations you're working to it might be interpreted as mandatory. I've never personally solved a problem by grounding an ungrounded system, but I have solved problems by removing the ground.
AutoMax, I have had the opposite of what you stated and have solve several issues by applying the proper grounding to systems that had intermittent problems.
  Reply With Quote
Old June 15th, 2017, 10:59 AM   #8
rupej
Member
United States

rupej is offline
 
Join Date: Sep 2014
Location: NC
Posts: 234
I have done it both ways but prefer to leave it ungrounded. I've never seen grounding solve a problem with noise or anything else. Not that I doubt that other people have.

Also it would seem to be hazardous to our delicate 24VDC electronics in the event of a major ground fault of nearby high voltage equipment.
  Reply With Quote
Old June 15th, 2017, 11:42 AM   #9
Mad_Poet
Member
United States

Mad_Poet is offline
 
Join Date: Feb 2017
Location: Virginia
Posts: 117
Talking about grounds.
Not a 24 VDC ground, but I have a 120 volt AC isolated ground system powering several computer systems.

Jackleg electrician tied one of the isolated grounds to the ground in another panel.
In two days I had two computers corrupt their files.

I had to get a REAL electrician to find it and remove the 'extra ground'.
Once my isolated ground panel was, once again, isolated (with only the ONE
ground) my computers were happy and corruption free again.

MadPoet.
  Reply With Quote
Old June 15th, 2017, 06:11 PM   #10
skyfox
Member
United States

skyfox is offline
 
skyfox's Avatar
 
Join Date: Nov 2006
Location: CA
Posts: 170
WOW! Seems 50/50. I was hoping for 90/10 sort of response. Thanks to all of you that replied. I guess more research is needed on the subject.

Cheers!!!!
  Reply With Quote
Old June 16th, 2017, 02:29 AM   #11
BryanG
Member
United Kingdom

BryanG is offline
 
Join Date: Feb 2005
Location: Manchester
Posts: 1,138
OK, can't believe I am being pulled in to this again. The danger of not earthing a system is that one electrical fault can go undetected but can kill someone, simple as that. If you choose not to earth the system then you must use a design system that separates the dangerous voltage and the 'safe' voltage so that no fault can ever cause them to meet. Generally it means separating the mains and controls in separate parts of a panel. If you have a mixed panel as most industrial boxes are with contactors switching mains next to relays working at 'safe' voltages then you must earth the secondary.

Quote:
but I have solved problems by removing the ground.
You didn't fix the problem you just painted over it with dangerous paint. The problem is still there, you have a lousy earth system that needs to be fixed, people have died because of bad earths.

Sometimes you have to have a floating system, but you must be very aware of the consequences.
  Reply With Quote
Old June 16th, 2017, 04:38 AM   #12
AutoMax
Lifetime Supporting Member
United States

AutoMax is offline
 
AutoMax's Avatar
 
Join Date: Apr 2017
Location: Indiana
Posts: 217
Respectfully, Bryan-

How do I keep hazardous voltage from being introduced on the load side of an ungrounded signal wire from (for example) auxiliary contacts on a motor starter overload? I totally understand what you are saying, but are you suggesting as a matter of course electricians should touch bare conductors without verifying the absence of voltage?
  Reply With Quote
Old June 16th, 2017, 06:16 AM   #13
OkiePC
Lifetime Supporting Member
United States

OkiePC is online now
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 9,411
I will only tie the 24VDC common to ground if required by some oddball piece of hardware in the system that has it done that way internally. I can think of one recent device like this that would lose its marbles if I didn't ground my DC negative side.

The only advantage I can think of aside from the above is that if you are troubleshooting a field device where the DC common is not present and you want to see if the right 24+ voltage is present, you can touch one meter lead to a good ground.

The disadvantages have already been described: 1) higher susceptibility to ground fault noise. 2) potential for false (sinking) inputs if a conductor shorts to ground.

There would not be a shock hazard with 24vdc. I'm with BobB on this but will make exceptions.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
  Reply With Quote
Old June 16th, 2017, 07:21 AM   #14
BryanG
Member
United Kingdom

BryanG is offline
 
Join Date: Feb 2005
Location: Manchester
Posts: 1,138
Don't worry you don't need to be respectful, I have had this argument many many times.

Quote:
but are you suggesting as a matter of course electricians should touch bare conductors without verifying the absence of voltage?
Don't think I said that anywhere.

Let me bounce a question back to you. Are you saying that you would be happy to stand up in court and say 'It would have been easy to design it to be safer, but he should have used a meter before going near that low voltage circuit'.

Another issue I forgot to mention before is that removing the earth connection may or may not create a floating system. Each component that has electrical noise filtering will have a connection between the supply and earth. I have found various devices that connect the negative to earth within the device. So unless you test each component you don't create a floating system you create an unknown system.

I am always open to hearing arguments and am happy to be persuaded of the error of my thinking. Bobs argument is that you loose isolation, I would say that if you are designing an isolated system and you understand the consequences of that design then that is great. But if you are leaving it unearthed because that is the way 'Fred' always designed them then you are heading for trouble.

I know that it is easy for me to tell people to fix their earth problems, I live in a wet country with a fairly solid supply system, others don't have that luxury.
  Reply With Quote
Old June 16th, 2017, 07:52 AM   #15
BryanG
Member
United Kingdom

BryanG is offline
 
Join Date: Feb 2005
Location: Manchester
Posts: 1,138
Quote:
The only advantage I can think of aside from the above is that if you are troubleshooting a field device where the DC common is not present and you want to see if the right 24+ voltage is present, you can touch one meter lead to a good ground.
It is safer, you are less likely to kill someone, to me that is quite a big advantage.

Quote:
The disadvantages have already been described: 1) higher susceptibility to ground fault noise.
So you are saying that you do it because it is easier, that is a really bad reason. Fix the earth problems.

Quote:
2) potential for false (sinking) inputs if a conductor shorts to ground.
Are you sure that your are not just trying to wind me up now. You shouldn't be using inputs that can be fooled by a short to ground fault with a negatively earthed supply, they are for positively earthed supply system. That just means you have bought the wrong input card for your PLC, or you wired it wrongly. Generally in the West we use a PNP system, generally in the East they use an NPN system, obviously that is very generalised.

I knew I shouldn't have got back in to this argument.

Has anybody got a reasoned argument about why it is safer not to earth the control supply output.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
OT: UPS neutrals OkiePC LIVE PLC Questions And Answers 15 December 17th, 2015 01:16 PM
Advice for connecting ground of RS 485 in PLC arbj LIVE PLC Questions And Answers 6 October 10th, 2015 01:30 PM
Single ended vs Differential learner LIVE PLC Questions And Answers 3 December 15th, 2010 11:34 AM
" do not care for AC connection " is this statement correct ?? magdyfayad LIVE PLC Questions And Answers 26 October 3rd, 2008 09:52 AM
Transformer wierd voltages leitmotif LIVE PLC Questions And Answers 32 September 21st, 2008 02:34 PM