1769-of8c tie to 24vdc- for common signal
g.mccormick
Jul 2012
IN
961
We have belimo valve that is getting powered by 24VDC power supply. That same power supply is feeding the DC+/- of a OF8C analog output module. Right now, I have a 500ohm resistor across the 4-20MA output to generate 2-10V. The issue is that if I measure the AO+ to 24vdc-, I get 34VDC. If I try and tie the AO- directly to 24VDC-, I fault the power supply... What am I missing here?
The PLC power supply is seperate from the 24VDC power supply powering OF8C and the belimo valve.
Follow up. It looks like they have some serious miss-wiring either in their panel or out in the field devices. I started pulling off field wiring and was able to find a few of the cables that were backfeeding voltage. Hopefully the high voltage on the valves did not damage them, but they were not able to get them to move.
Good Afternoon , I'm going to be replacing a few SLC 500 PLC's with CompactLogix this year. I would like to keep the PowerFlex 70 Drives in...
2,123
Hi all, I have a 1769-OF8C (analog outputs module) whose light is blinking. According to the manual, this means "external power failure"...
1,658
Good Afternoon , I have some new machinery that I need to tell another machine what speed I am running. The analog output card that I am...
2,714
Hi everyone, Today I created an algorithm in the PLC of the pulp plant where I work at, what I need to do was to match the flow of a screw pump...
3,225
Good day all. Quick question just to confirm my suspicion that I have a failed output card. Current output, 4-20ma, 24VDC supplied to card...
1,460