1769-of8c
PLC Pie Guy
Jun 2013
Halifax
1,144
Good day all.
Quick question just to confirm my suspicion that I have a failed output card. Current output, 4-20ma, 24VDC supplied to card, output channels see 10.4 VDC and 0ma.
Problem?
I should mention this is the result of a fuse blowing that supplies the card with 24VDC, I think at this point from water penetration.
I got this!
Turns out there was a broken connection on a resistor that was installed at the instrument connection point. Plus the box was full of water and corrosion, hence the strange readings from the output.
Live n learn!
Good Afternoon , I'm going to be replacing a few SLC 500 PLC's with CompactLogix this year. I would like to keep the PowerFlex 70 Drives in...
2,123
We have belimo valve that is getting powered by 24VDC power supply. That same power supply is feeding the DC+/- of a OF8C analog output module...
1,746
Hi all, I have a 1769-OF8C (analog outputs module) whose light is blinking. According to the manual, this means "external power failure"...
1,658
Good Afternoon , I have some new machinery that I need to tell another machine what speed I am running. The analog output card that I am...
2,715
Hi everyone, Today I created an algorithm in the PLC of the pulp plant where I work at, what I need to do was to match the flow of a screw pump...
3,226