Good afternoon ya'll....looking for someone who has a good handle on the load memory siemens uses, aka the MMC cards that are inserted and are required for CPU operation.
The problem I have, is under the CPU Messages....The load memory appears to be 96% full. The work memory is only at 32%. I still have to add some logic to the Processor...will the load memory be affected by that?
If I was to add a larger MMC to the processor, would that take care of the problem? I don't know if that 96% is the load memory total, or just on the CPU....(is it counting the MMC in that load memory calculation). Also, will the compression compress the Load Memory?
Any comments would help. The machine is in a faraway land, and I cannot access the CPU remotely.
Thanks in advance guys!
Hayzed1
Hi guy, sorry for my English
With my experience there are two types of memory for cpu, the one is program storage memory (such as MMC) and you can expandable, the other one is program executing memory (load memory) and you can't expandable because it depending on cpu version, for your problem you must upgrading your cpu to higher version.
I hope this message will help you to fix
Hayzed1,
the load memory can be expanded, it's the MMC you mention. The work memory is the internal memory of the CPU and that cannot be expanded. In recent CPUs (the ones with the MMCs) you can store the entire project on the MMC, including the comments and symbols etc. Maybe you could test by removing comments if the load memory is sufficient as is, but removing comments is definitely not something I would recommend as a finished state. The best solution is of course to get a bigger MMC and install your project on that one.
Kind regards,
- no cpu required for load memory upgrade, but for work memory
- jvdcande is right, you can buy just bigger MMC card or
perform some optimizing ( plenty of them possible :) )
- if you were performing some tests, maybe you could forget
few (data)blocks in memory (sometimes happen to me then i'm
testing new methods) just open station online and check it
What CPU are you using??
Go to the Simatic Manager> right click on the blocks folder> Object Properties> Blocks
Check and see how much load memory and work memory your project uses.
I'm sorry to disagree with some points. With Siemens S7-300 CPUs you can't expand load or work memory so, if you buy a bigger MMC you will spend more money and get more space only for writting files, not for program. If you really need more memory you need to replace the CPU.
If you compress the memory both load and work memories will be compressed.
If you need to replace the CPU why not try one VIPA CPU? You get more memory and you don't need the MMC because both work and load memory are already integrated.
Dear all, In the attachment this is a complete recipie management in Siemens S7 PLC. The recipie management using the load memory (PLC memory...
1,788
I'm trying to get a handle on what is "Load Memory". Can any one explain what Load Memory is and how it is implemented?
13,629
Hey guys, I have to take an upload of a program on an S71200 PLC to change a hardware config option and then redownload the program with this...
127
Under PLC tags it shows there is a discrepancy with a lower level component via the orange exclamation mark. Yet there is no Blue/Orange under the...
595
Hi All, I'm new to Siemens PLCs. I have a device that have a Siemens 1515SC IPC ruining the control and HMI applications, its documentation...
1,733