modbus hmi modbus tcp reads from a wago 750
ganutenator
May 2002
kansas
1,440
Probably something simple, but my project hmi (schneider mounts in a button hole hmi) doesn't seem to be able to read or write to my wago plc.
The plc and hmi project was developed in So Machine and I translated the so machine into codesys for the wago 750 (tough job, I know, right). So I expected the hmi to at least be able to read or write to something.
What addresses are you trying to write to? Holding Register Word 0 in the PLC = 12288 in the HMI
thanks!
That worked.
why the offset?
More importantly, If I want to read %MX0.15? Would that be %MW12288.15?
I assume the offset may have something to do w/ registers allocated for I/O?
It comes from this table
Your syntax for bool is correct
I was tasked w/ evaluating the schneider m251 w/ so machine vs the wago 750-852? w/ codesys.
Wago totally won via dif. from to ports on the port forwarding (aka multiple machines at one site), 0-15 bool vs scheider's 0-7 bool thingy.
I have a Red Lion G09 scanning 8 Invertek P2 VFDs via modbus RTU - I've setup necessary comms and tags and all works well. I have a 'Settings'...
1,873
disclaimer- 1,no one in their right mind would pick this configuration but I want to try and get it working. 2, my MB knowledge is sketchy at...
1,142
I am trying to get a Mitsubishi GT2715 HMI to read and write from a Eurotherm 3508 controller using 4 Wire RS485 Mobus RTU communications. The...
1,309
Well, I'm working with this ABB plc project, and It's been a learning experience coming from Allen Bradley. The project can't be changed to an AB...
1,176
Hi everyone, I'm hoping someone has some experience in this because I'm at wits end ready to tear my hair out lol. I have a SP5000 Series Proface...
1,957