Panelview Help

ngilbert

Member
Join Date
Oct 2017
Location
Ohio
Posts
28
Ok I’m ready to pull my hair out.

Trying to get a PanelView800 to communicate with a 1769-L33ER PLC.

Doesn’t seem to want to cooperate.
PV 154.269.77.139
L33ER 154.269.77.141

Have the controller entered as 154.269.77.141,1,0 in connected components workbench. Anything I could be missing or doing wrong?
 
Do you have "CompactLogix 5370" selected for Controller Type?
edit: Also, what version of CCW?
What version does it show for the terminal in the settings page?
 
Also, in the comms path top the controller you have to add I.P. whatever,1,0...


Capture.PNG
sPIiJq1AAAgFoIeQAAxRDyAACKIeQBABRDyAMAKIaQBwBQDCEPAKAYQh4AQDGEPACAYgh5AADFEPIAAIoh5AEAFEPIAwAohpAHAFAMIQ8AoBhCHgBAMYQ8AIBiCHkAAMUQ8gAAiiHkAQAUQ8gDACiGkAcAUAwhDwCgGEIeAEAxhDwAgGIIeQAAxRDyAACKIeQBABRDyAMAKIaQBwBQDCEPAKCYJFnZMDv+5aYZJIk9UXVlw5ZuDqrni2sAAGCesZntgnzTbKyIULfsbKxkx3nZiknzvloPAADmFWP+HxY5fI5HpEs5AAAAAElFTkSuQmCC
 
Last edited:

Similar Topics

I've adjusted the IP of the Panelview Plus as well as the DNS servers; the screen does not show up in the search when I go to the transfer utility...
Replies
3
Views
94
Can anyone help out with this Panelview Plus Performance Email. I keep getting an "unable to activate connection "smtp-mail.outlook.com". I've...
Replies
4
Views
236
Hi all, I'm in the process of upgrading a PanelView1200 HMI program to be developed in FactroyTalk View Studio. The filetype for PanelView 1200...
Replies
7
Views
315
Ive got an existing panelview plus 1000 with a logic module of 2711P-RP and an assembled pn of 2711P-T10C4D1 running out in the field. Its in an...
Replies
5
Views
1,212
Hi all, we have several identical machines running allen bradley plc's. they are all the same, same bit addresses, timers, counters. same...
Replies
3
Views
1,408
Back
Top Bottom