Clarifications regarding RLO in STL in Simatic Manager
orense, I want to confirm this statement. Was the value of M7.0 changed or was the state of the RLO at the execution of M7.0 changed? Those are two very different things.
This is the part that I was confused about as well.
Originally posted by L D[AR2,P#0.0]:
To clarify - a new network will not affect the logic processing.
That is completely different than what I would have thought. So what does separate logical units? Is it the assignment? That would mean you wouldn't be able to make multiple assignments as a result of a single logic segment so I suspect it is something else. I would have thought it was the network indication but apparently not.
Keith
From the siemens help on STL
Code:
/FC        First Check Bit (Status Word, Bit 0)
 The /FC bit signal state controls a logic operation string.
 The /FC bit is status word bit 0.
 Each logic operation queries the /FC bit signal state and the
 addressed contact.
If the /FC bit signal state equals ‘’1,’’ an instruction
 logically combines the result of its signal state check on its
 addressed contact with the RLO generated since the first check
 and stores the result in the RLO bit.
 If the /FC bit signal state equals ‘’0,’’ the logic string
 begins with a first check.
 The logic string ends and the /FC bit is set to ‘’0’’ with
 the assignment of a value (S,R,=) or with a RLO-dependent jump instruction.
The =,S,R instructions use the current value of the RLO but do not modify it, hence you can have as many assignments as you like at the end of a logic "string". The first check comes into play with the first logic operation after the assigments.
Dear All, I am Using Omron CPM 2A PLC in a Application. This controller has 2 ports a) Pheripheral Port and b) RS 232 Port. Pro Face HMI...
5,065
1.Why RS 232 cannot be used for multidrop applications? 2.Why RS 232 can be used only up to 15m but RS 485 for longer distance? 3.Which factor...
3,239
Hi everyone, I need a solution based on the cause and effect diagram, especially a macro sheet or VBA script in Excel, which will help me generate...
88
I know this can be done, but I can't get the router config right. My goal is to physically connect(using an ethernet cable) a device(PLC, RTU...
1,065
Hi, I am connecting an Autonics make stepper driver type, MD5-ND14 to a Kinco PLC (K205 series) this has a sourcing output which cannot be...
1,144