Testing ControlLogix and CompactLogix CPU's without I/O
Rob S.
Sep 2008
Maryland
739
Good Morning ,
We have a shelf of ControlLogix and Compactlogix CPU's . I would like to test these and also use these for training . Can you download a program to them , same processor in the program application as what I would be trying,
without I/O ? Explained another way , just plug it in a empty rack , and download the program .
Thanks for your help ,
Yes, you can. The only stipulation is that the processor be in the same slot in the rack as the program calls for.
For best results, go into each I/O module's configuration, and on the <Connection> tab check the "Inhibit Module" box. Now the processor won't try to scan those I/O non-existent I/O modules, and you can write (by hand or programmaticly) any value you want to the Input addresses to simulate a response.
I personally prefer to simulate by writing to the raw input addresses ("Local:3:I.x") rather than having two separate "mapping" routines -- one for real I/O and one for simulated. YMMV.
Have fun!
Hi Guys, Can ControlLogix with Modsim32 for Modbus Server Testing? I have ControlLogix via Anybus Modbus TCP and I need to Test the...
321
I am working on setting up a Prosoft Datalogger model PLX51-DLplus-232. This unit will be collecting data from a SLC 5/05 on the DB9 port set to...
104
Hi all, I have a AC current transducer that I want to bench test to ensure I am getting a 4-20mA output. I am using a AE001 unit. It is very...
119
Hello all, looking for ideas on getting some basic training done, I need to practice on maintenance timers and bypass switches (with a Factory...
1,318
I have a project in FTV ME (Studio v13) that I'm trying to apply security to a few buttons/setpoints. I have 4 users: Anonymous Logon, DEFAULT...
789