DCS Instruction fault with Keyence SZ-V32NX area scanner

OK, so finally figured out this part.

The problem was with using the DCS Instruction. DCS Instruction is only for use with non-OSSD redundant inputs.

If OSSDs are involved, we must use either a hardware filter for the self-test pulse, or use a software filter.
In order to use a software filter, we can use the LC Light curtain instruction. I started using the LC Instruction, it works fine. Glad a fix was found.

Regards,
-PreLC.
 