Help with DCS instruction.

HoldenC

Member
Join Date
Sep 2012
Location
Cumberland, KY
Posts
220
I have a DCS instruction, that is set up for an E-STOP. I have the restart type and cold start type both set as automatic. I can test the e-stop and it works as it should. However, after a power failure, the instruction wont reset. Channel A and B are showing as 1, but the CombinedINputStatus is still reporting as a 0.

I have jumper out the "01" bit from the DCS and then it resets.

I have attached a snippet of what I'm talking about. Can anyone help me understand why the CombinedInputStatus isnt changing state ?

DCS.png
 
CombinedInputStatus is a status bit of the safety input card that is an AND of the status of all inputs on the card. As such, it will be off if any of the inputs on the card are faulted, not just the two you have wired for this particular e-stop.

Most likely you have other things wired into the card that are errored until e-stops are cleared.
 

Similar Topics

Good day, I need help regarding how to communicate a DCS that uses controlnet for their HMI interface and I/O communications. Can the controlnet...
Replies
4
Views
2,440
hey all i have a problem finding info and examples of the EMERSON Ovation system Online , does anyone knows where to get some info?? or had...
Replies
4
Views
7,641
I'm confused. Is a DCS (Distributed Control System) a multiple PLC setup in a distributed control configuration or DCS is a kind of controller...
Replies
4
Views
1,668
So i've been at this for a long while, i have Citect Scada 2018, i have full access to everything but i can't seem to find any option or...
Replies
0
Views
23
Hi all, hope you are having a great day, I am in need of your help to create a AOI or program that does this kind of job: I have a IO Link...
Replies
9
Views
141
Back
Top Bottom