DCS Instruction fault with Keyence SZ-V32NX area scanner
OK, so finally figured out this part.
The problem was with using the DCS Instruction. DCS Instruction is only for use with non-OSSD redundant inputs.
If OSSDs are involved, we must use either a hardware filter for the self-test pulse, or use a software filter.
In order to use a software filter, we can use the LC Light curtain instruction. I started using the LC Instruction, it works fine. Glad a fix was found.
Regards,
-PreLC.
I have a DCS instruction, that is set up for an E-STOP. I have the restart type and cold start type both set as automatic. I can test the e-stop...
396
Hello, I am using the DCS instruction for a simple emergency stop detection. Actually I set the "cold start type" to automatic. This means when...
2,493
Hi everyone How i can configure a periodic report of the list of alarms? Thanks
100
Hi Everyone, I am currently trying to communicate ControlLogix PLCs via EtherNet/IP with Delta V DCS. There is a VIM2 card configured for...
287
Hi, I need to read three 4-20mA signals from a DCS(ABB) in a remote 6 channel analog input module with RS485 modbus port. When I connected...
492