S7-200 High speed counter
bill4261
Jan 2005
mid-west
99
In my high speed counter setup I've attached the interupt the move the counter value to a temp register and zero the counter. I think my counter is missing counts when this reset takes place. Has anyone else had this problem?
I don't have any experience with the S7-200 but I will try and help you anyways.
Why exactly do you think it missed counts? What are you basing this on? What is the frequency of the signals being counted?
There are few problems that haven't been seen before.
It is too bad the counter card designers have reset inputs instead of inputs that latch the current counts. The designers made it very easy to do the wrong thing which is a violation of Delta rule #2.
There is an answer in there somewhere. You just have to search for it.
I'm reading a mark on a cylinder. That mark should produce the same number of counts every time around. The frequency is less than 5K.
I would push it to a Global data point and avoid the TEMP area. When you return from the interrupt the previous temp area gets restored.
I would also not reset....just stamp the value and calculate the difference.
Nick
Not sure how you do this in a S7-200 but; Store the count value on the interrupt event and then take away the stored value from the running counter value. So the counter never stops.
I was on the path of not resetting the count and calculating the difference as Nick B suggested. I will have to reset the counter at some point.
I have a current project replacing S7-200 PLC with S7-1200 PLC (6ES7 215-1AG40-0XB0). The program conversions are manually created. I just want...
1,754
Looking for example of the use of the HSC in a CPU 1212C PLC. Not sure of how to establish Hardware ID, and which input to use the ID1000 is it...
1,846
Hi everybody, I would like to start by letting you know that i'm a begginer in PLC programming and i can use a little help here, please. I'm...
1,592
Greetings, I am trying to get a Incremental Shaft Encoder (white pages attached) to count on my HSC in my 1200 project. I have assigned the first...
17
12,950
Hello everyone, I got a question about the High speed counter It needs to move out a slide when the count reaches 100pules, and it needs to move...
4,146