plc 115vac input

rick62

Lifetime Supporting Member
Join Date
Jul 2013
Location
tuscumbia al
Posts
45
I keep losing this input on an dl06 automation direct plc, all inputs are 115vac, all of the other ones are ok, just one that I have had to move twice to another input- what is the best way to protect your 115 vac inputs from failing.
 
I keep losing this input on an dl06 automation direct plc, all inputs are 115vac, all of the other ones are ok, just one that I have had to move twice to another input- what is the best way to protect your 115 vac inputs from failing.

What is that input coming from? Can the device you're monitoring create an inductive spike when it turns off? Can you use an interposing relay on that input?

A properly rated MOV in parallel with the input, and connected to ground may help.

-rpoet
 
Since we're talking about it, can anyone recommend a MOV or snubber they'd recommend to put across the coils?

I tried picking one out on Mouser a few weeks ago, but all the choices are overwhelming.
 

Similar Topics

The past week we received a new piece of equipment from Germany which utilizes siemens controls. Typically in our company we use A.B. controls for...
Replies
4
Views
40
the conveyor can stop because of a safety sensor or safety switch. And also it can stop because of an object jam detector sensor. If the conveyor...
Replies
5
Views
119
Good Day to all of you, this is my first post, i will try to explain as best as possible, english is not my natural language. I am performing an...
Replies
0
Views
29
Hi All, Someone at work has put a PLC system on my desk, that's just been taken off an idle production line. He said "It's an S7 PLC. We don't...
Replies
10
Views
189
I have a project to automate four generator sets. The system will monitor and store the load demand of the factory. Once there's Power outage, the...
Replies
0
Views
55
Back
Top Bottom