Help for Guard Logix CPU L71S

Ali Raza

Member
Join Date
Oct 2016
Location
Lahore
Posts
16
Help required For Guard Logix CPU L71S

We are facing following problems for gurad logix

1) How we can edit the safety Program and safety tags

2)Could not change the Safety Modules Properties

Is there is any procedure for that or it is software end Problem using Studio 5000 standard edtition

After that we send Empty program with Existing Hard ware then At online it gives I/O Not OK communication not established bw EN2tr to AENTR and its safety point ios
 
You have to unlock the safety to change anything safety related....in the upper left of logix while online does it show locked or unlocked?
 
You can't modify any safety programs using Logix Standard Edition. You will need Full or Professional edition.

And, as robertmee said, you'll have to have the safety unlock password too.
 

Similar Topics

Hello, I'm adding an Allen-Bradley SensaGuard door switch (440N-Z21SS2H) to a small existing machine to drop out pneumatic function when the...
Replies
3
Views
1,004
Hi to the forum. I have a logic problem which is confusing me. From my sketch I have seven conveyors that I control using a twido PLC via canbus...
Replies
19
Views
5,627
I've adjusted the IP of the Panelview Plus as well as the DNS servers; the screen does not show up in the search when I go to the transfer utility...
Replies
3
Views
99
Hi Everyone, I own a GE Versamax controller that I purchased for a class at Long Beach City College a couple of years ago. I lost the use of my...
Replies
7
Views
126
I was wondering if anyone could help i am trying to use a SLC 500 with a 5/05 processor to set up an incremental encoder to a HSCE2 card? The card...
Replies
2
Views
154
Back
Top Bottom