needed little help with the connection of VFD and setting its parameters.
Delta series B VFD (3 phase, 2.2 kw) used to vary the speed of conveyor.
Control signal (Fw, RW, Ov, Analog signal (0-10v)from plc, inveter also give signal to plc when it is on)
I have connected these signal as follow.
Fw to the FWD terminal of VFd.
Rw to the REV terminal of vfd.
Ov to the DCM terminal (for sink mode)
Analog signal 0-10 v to the AVI.
24v to the RC (Relay common)
X which is giving input to plc connected to terminal RA (Relay output(N.O.).
IS it correct ? and what parameter needed to be set.
Delta series B VFD (3 phase, 2.2 kw) used to vary the speed of conveyor.
Control signal (Fw, RW, Ov, Analog signal (0-10v)from plc, inveter also give signal to plc when it is on)
I have connected these signal as follow.
Fw to the FWD terminal of VFd.
Rw to the REV terminal of vfd.
Ov to the DCM terminal (for sink mode)
Analog signal 0-10 v to the AVI.
24v to the RC (Relay common)
X which is giving input to plc connected to terminal RA (Relay output(N.O.).
IS it correct ? and what parameter needed to be set.