Hi!
I'm an intern and a newbie in the field of automation. I was given the assignment to learn and program a PLC and HMI together.
PLC: Delta DVP80ES200R (DVP ES2)
PLC Software: ISPSoft 3.17
HMI: Delta DOP-112WX (DOP-100 Series)
HMI Software: DOPSoft 4.00.16
The problem I have is that the HMI and PLC don't communicate properly. The HMI sends the data to the PLC but the PLC doesn't send its' data back to the HMI (ex: If I press the M0 button at HMI, Y0 lights up in the PLC but the Y0 indicator in HMI does not).
I've been following this connection of HMI to the PLC: https://deltronics.ru/images/manual/DOP-112-115+Quick+start+manual_EN.PDF. It's currently connected by RS-485 COM1 (HMI) to RS-485 COM2 (PLC).
If you have other questions, feel free to ask me.
Thank you in advance!
Hi!
Apparently, from what you have said above, if the output Y0 lights up when you press a button on the HMI, it seems that you have communication between the PLC and the HMI.
I would check the indicator object and namely the setting for the indicator lamp. Check the mapping and the type of indicator you chose.
Best Regards
Konstantin Kolev
As the previous post it is probably something to with the display object, if the communications was not working correctly I would think that you would get com errors poping up.
Hey guys,
Thanks for the help. As Konstantin mentioned, the problem is in every object's read/write address. I knew it was a dumb problem. Thanks again!
Hi Friends, I have CPU315 2PN/DP configuered as shown in the images attached. It is connected through profibus network to PC477 & which acts as...
2,917
Good Day to all of you, this is my first post, i will try to explain as best as possible, english is not my natural language. I am performing an...
46
Hi, We have a customer that has an old DOP-A80THTD1 that is needed to be upgraded Can we upload from these units? Is there a special...
98
Hello, I know little English, I want to use 4 plc cqm1 as slave (modbus), and hmi delta as master. Unfortunately, I cannot establish rs485...
590
I'm trying to establish communication between an HMI DELTA (DOP-B07E515) and a PLC IDEC (FC6A-D16R1CEE) via the RS-232C/485 module (FC6A-SIF-52)...
576