I just programmed a PID control system for a VFD to control header pressure for our weak liquor pump to our evaporators. I tested out all the motor control logic as well as tested the adjustment registers for the the set point and output logic with the Delta-V HMI. At this point I did not have the PID enabled because I was not ready for it. As soon as I enabled "B3:1/0" which enables the rung to the PID the Processor Faulted and it damn near took the Evaporators down. I attached the program so you guys could have a look and see what mistake I have obviously made. Please help as I'm expected to commission this system tomorrow afternoon.
Thanks, Tex
** edit, I noticed that the process variable for the PID I used is also used at the PV for another PID and I also had forgot to set the Update time for the PID. I don't know if this helps but I thought I'd try.
I don't have software available right now to look at your program, but you almost certainly have an out of range number in one of your PID parameters.
I think I got it figured out. I had the timer in rung120 set for 1 second to update the PID Loop time. But in the PID I had a value of 0 entered for loop update time. I have a test rack and processor in my office and downloaded this program onto it and when I enabled the PID it faulted and I got a chance to look at the fault and it said I had "entered a negative time value in a PID instruction". Once I cleared the fault and put in the update time as "1" I put the processor back into Run mode and no issues. I feel like an idiot :( definite learning lesson!!
It got me once. After that, I was very careful to check all of my parameters before enabling a PID instruction. An SLC will do the same thing.
I have a PLC 5 that has a faulted processor, can some one tell me how to see why it is faulted and how to reset the fault? I have not messed with...
2,396
Good Evening . I visited a pump station sight today that has a PLC-5/11 CPU. I was given a CD with only a file with a program and extension of...
3,813
Hi friends, I am AVI , working on Schneider electric make M258 PLC. While communicating it with SO machine software v3.0, facing problem...
1,336
Hey everyone, I can't seem to find good instructions on how to connect/set up a brand new PLC. Thanks for the help.
2,722
Hi there, I am confused with configuration of these modules.My queries 1. Do I need a communication module( NOC0401) to identify the PLC and...
3,645