M340 PLC: BMXP341000 Processor and BMXNOC0401
dev78386
Supporting Member
Sep 2016
Australia
24
Hi there,
I am confused with configuration of these modules.My queries
1. Do I need a communication module( NOC0401) to identify the PLC and program.
I am using a USB Type B to program, as the processor has a serial port and Modbus Port.
2. Do I need to setup the NOC0401 module to transfer the program in to the PLC
3. What is the communication module for as i am able to transfer the program in to M340 PLC using typeB connector on the processor module.
4.When I am configuring the communication module which family processor I have to choose. I know that it opens up with a default. However, I cannot see the P341000 family of processor in the drop down menu. I watched youtube videos where everyone changing the family from default to P342000. I am struck here as I have a P341000 processor. Confused!
Previously I have successfully configured AB 1400 PLC, where I used a serial port for programming and IP configuration to identify the PLC. Is it the same with schneider M340 as well?
I am missing some theory and logic. can someone please briefly explain.:eek:
Thank you
Immanuel
Hi there,
Thank you
Immanuel
1. You Don't necassarily need a NOC Module, its an extra ethernet module, they are normally used on M340's if you need 2 PLC's to transfer data to each other, the CPU ethernet port does not have that functionality.(I0 Scanning/Global Data)
2. You dont have to set it up, but if you have one you probably should.
3. see number 1.
4.The P34 1000 should be the very first module under the Modicon m340 tree when creating a new project or changing the processor, what version of unity are you running?
You Can use the USB port with full configuration and programming functions, when you connect select USB and the address will be SYS.
you only need properly shielded USB cable, cheap USB cables aren't allways working.
Schneider have own cable, where shield can be earthed, but that isn't userually needed.
Just to clarify a NOC module is for communicating on ethernet IP and/or Modbus TCP IP
networks. Once it is configured you can also program and go online via ethernet (NOC) to plc
Hi friends, I have programmed an M340 PLC (BMXP341000 Processor) using Unitypro XL and ran out of the trial period. Yesterday I installed a...
2,124
Good day, I have an issue between an M340 PLC and a PRA 0100. The problem is as follows: I have a communication link between the PLC and the PRA...
834
Hello, Not able to find Modicon DO modules BMXDDO3202 in EcoStructure Control expert V15 catalogue. But i can find only MBXDDO3202K. Can you...
477
so i have an isssue where if the serial port of an M340 plc disconnect from the screen it would retain the values of the variables being sent...
922
I need to establish communication between Schneider M340 and S7-1500 PLC. I am using gateway converter for MODBUS TCP TO PROFINET protocol...
3,019