Modicon TSX Microscan to AB Micrologix communication
kulkago1
Jul 2006
Goa
We are trying to interface Allen Bradley Micrologix1100 with Modicon TSX Microscan through Modbus.
Micrologix is Master and Modicon is configured as slave PLC.
This connection is to Modicon's D+ And D- terminals.
All communication parameters are matched with both the PLCs.
But communication is not getting established.
We see blinking of the LED on Modicon communication card but no dat is received from Modicon.
Can anybody help to resovle the issue?
I don't know how it's done in this Modicon but I seen in another Modicons following: if Modbus request tries to access not allocated %M or %MW communication fails. Check your 0x, 1x etc. allocation.
Everything was working fine, but suddenly CPU went into error mode, and the ERR and TER LEDs lit up. Now I can't download or connect with the PLC...
39
After updating a panel, I inherited another PLC for my "learning lab". It's a Modicon TSX Micro. I've not worked with a Modicon PLC yet, so I...
135
Hello I was needing help with the proper scaling on a Modicon TSX Quantum- AVI030-00 8 Channel Analog Input PLC card. What would be the proper...
1,480
Pure mind boggled at this one, can’t seem to figure it out. NO contact with - %M130(%MW11) How is this possible? Is the %MW11 0 it’s logic 0, 1...
1,533
Hi All, i have PLC Modicon TSX 3722 Micro i need to know where should i put the socket of programming cable on Ter or Aux port. and i see the file...