FactoryTalk View SE as OPC client with Kepware OPC server
nikhilec2007
Dec 2014
Gujarat
36
I have an energy Conzerv EM6400 meter giving data on RS485 modbus and Kepware OPC server taking data via MOXA RS485 to Ethernet converter.
Now I want to take same data on FTView SE.
Note that KepWare and FTView SE are on different PC on network.
Is there any way to configure FTView SE as OPC Client which can take data from KepWare OPC server?
Is there any other solution in your mind, please let me know?
Any ideas?
Yes your post does contain basically everything you need.
You can use the same configuration with the Moxa and Kepware OPC server.
In View SE you right click on your View SE server -- Add new server - OPC Data Server
It will display a popup and you can select Remote OPC server and select the computer where the Kepware OPC server is installed. Then enter the OPC Server namd(ProgID).
I´ve used it with an INAT opc server and it worked well.
Regards
Neil
Hi everyone! I have a problem with FTVSE9.0 and Third Party OPC, i cannot read tags from opc server (KPEServerEX), and i do it without problems...
5,613
Hi - quick question. Can FactoryTalk View tags (HMI memory tags) be read via an OPC client ? I've setup a test FactoryTalk project with a couple...
2,403
Hello All, I need to add a SLC500 to FTView Studio and have run into a roadblock. The OPC topic is configured in RSlinx without a problem, but...
3,924
I tried doing this by adding a remote opc server running wonder ware on an Opto22 controler using ethernet. The topic comes through and is active...
2,127
Hello dear experts! Please advice me how to generate a digital alarm in FT VIEW SE A&E by one bit from a tag in KepwareOPC where this tag is a...
3,346