Hey fellas,
Just curious. If I set up a GSV in my RSLogix 5000 main program for a ControlLogix processor to get last or max scan time, will the returned number include the time taken while interrupted by the STI, that is, does the clock continue to run while it's off doing the STI or will the clock pause while it's off processing the STI?
Basically, I'm looking for total scan time.
The GSV can read the Task or Program execution time, and it returns the real-time it took to execute the Task or Program.
So, in answer to your question, yes, the times will include anything else the processor has to contend with, so you will get the overall Task or Program execution time.
Incidentally, the STI in ControlLogix are called Periodic Tasks, you can have many of them all triggered at different rates.
In ControlLogix, you can have 32 tasks in total, if you use one (and most people do), you can only have 1 Continuous or Cyclic task.
TY, it is an animated .GIF, but they don't work on here...
PM me with your email, you can have it....
Is there a way to know which is the primary and secondary chassis through gsv? I have read that "PhysicalChassis" (Chassis A/Chassis B) is an...
2,229
I am writing some GSV's to get the status of our redundant contrologix for display/alarming on the SCADA system. I have found the GSV's for...
8,222
All I am studying a PLC program from another facility. It uses an SSV instruction and a GSV. Data in SSV, GSV as follows...
7,407
Hello all, I've read a number of times on the forum that excessive use of the GSV function is to be avoided. Does anyone have any further info on...
2,099
Hello, I'm working with a CLX L72 CPU. I am using several GSV instructions in my program for communication health monitoring within my DLR...
7,805