Troubleshooting Experience - Muting a Light Curtain
rguimond
Jul 2009
Escuminac
666
This will be a bit long-winded, but it was a good learning experience and may be helpful to someone else...
To guard the exit of an automatic shrink-wrapper, we installed a set of light curtains and a light curtain controller (http://www.automationdirect.com/adc/Shopping/Catalog/Safety/Safety_Relay_Modules/Light_Curtain_-a-_Safety_Mat_Controllers/BH5902-22-01MF2-61) from Automation Direct. The documentation provided with the hardware was sketchy, but the on-line material was decent. We set up the components on the workbench for testing purposes. To eliminate the need to set up four muting sensors, we just used four N/C switches.
After connecting the components, setting the dials to the proper position and lining up the light curtains, everything worked as expected. If we depressed the switch representing MS1 and then the one for MS2, the light curtain was muted. Moving to the final position should be easy, right? Not!
Everything was set up in the wrapper control panel, but the controller would fault as soon as MS2 was blocked. Wiring was double and triple-checked and was found to be correct. Thinking the solid-state relays in the photo-switches were and issue, we replaced them temporarily with the NC switches used on the bench - same results.
Stumped, we took everything back into the shop and re-connected. It worked.
Back at the wrapper, we re-installed everything and... it didn't work. Same symptom.
Thinking the controller may be intermittent, we replaced it with a spare , but it still didn't work.
The wrapper is in a refrigerated milk storage room, so we thought perhaps the cabinet was too cold (specs call for 0-50C - we were at 3-4C), so we temporarily installed space heater. No luck
We used the original controller and re-connected everything in the shop. It worked, so we transferred every connection to the spare controller still in the cabinet one wire at a time. Fired it up and it didn't work.
Back to the manual (http://www.automationdirect.com/static/manuals/safetyrelays/bh5902_01mf2.pdf), I noticed that the MIN current from M1 & M2 had to be at least 25mA with active lamp. Thinking that perhaps the LED pilot lights we installed weren't drawing enough, I connected a second LED in parallel with the one installed in the cabinet cover. Muting now worked. Relieved, I decided to replace the second scabbed-on LED with a resistor. As I was loosening the connection screw on the original LED, I noticed the tag - 120VAC. It should have been 24VDC. The LED had too much resistance to allow 25mA to flow with the 24VDC control power from the controller! That was a whole day wasted, but a great learning experience.
I bet we all know that feeling...the combination of elation at having finally cracked it, and the sinking feeling of "I just wasted a whole day because of a f***ing 120VAC pilot light"
Have yourself a beer, it's the only solution 🍻
It brings to mind a similar, yet opposite, situation a few years ago. While fitting out a Faroese fishing vessel, we installed a small electric cooking range. During sea trials, we decided to boil some water for coffee. The infrared burner heated up INSTANTLY and we were all impressed how quickly the water started to warm, until the burner failed. Turns out the purchaser got a range for 120VAC supply instead on European-standard 220VAC. I was somewhat disappointed it didn't fail in a more dramatic fashion!
Hi all, Client called saying that the turbidity readout on the HMI is 0.0000 but on the local readout, it shows an actual value. Sure enough...
5,413
Quick question relating to my job search. Some job descriptions state "PlC troubleshooting experience" as either a requirement or a plus. What...
10,934
Hey when I turn on my Siemens PLC CPU 216-2 after runing 10 minute it's stop and showing SF indication after I turn off and some time later turn...
120
Good Morning , Not sure how many use Markem-Imaje SmartDate X60 Printers , but I'm having trouble finding a good manual for...
605
I'll preface this by saying this is the first time I've worked on a Siemens system and I'm fairly unfamiliar with them. I might mess up some of...
29
743