I wanna scale a 4-20mA on a siemens plc
I have 0 to 27648 on the analogue input
so what I do is:
I Devide the input with 27648. So at 20 mA I have 1 as result.
I multiply is with a range of 16 (4 to 20mA).
After that I Add + 4 (Offset)
Then I have scales 0 to 27648 to 4-20mA
How do u guys do this?