Error 78 on DeviceNet Scanner
apexpower
Feb 2009
Alberta
There seams to be an intermittent error that comes up ever few days. This error code says the scanner lost the scan list...is this a common problem? Could the problem be the DeviceNet scanner module or a corrupt Scan list???
If this is an Allen-Bradley scanner error 78 refers to a node in the scanlist dropping off the network. Typically it will flash the error code "78" followed by the node number "0-63" that has dropped of the network. Odds are you have a loose or bad connection to the node or nodes that are dropping off of the network. I would say it is not your scanner card if this is an AB system.
Hi all, Our cell was running ok then our scanner dropped out with error 80 idle mode. We got it running again but not sure what is causing it to...
3,533
I have a customer with Devicenet, currently having an error code E#77 show up on the scanner. The scanner in question is a 1756-DND. There are 20...
6,088
Hi All I have a question about devicenet on Compact Logix processor where i got two scanners. First is master second is slave. When i plug cabel...
4,734
I just tried to replace a proximity sensor on our devicenet, and i was able to commission the node and programmed the correct node number on it...
699
We replaced a VFD for a customer. The old VFD was a Fuji/GE G11 on a DeviceNet network with a bunch of other equipment talking to a SLC plc. I...
3,009