I just tried to replace a proximity sensor on our devicenet, and i was able to commission the node and programmed the correct node number on it, but now it flashes 83.The light is green on the device i installed.
the setting needs to be changed to polled
I figured it out that it needs to be polled, rather then strobed. how can i change it?
no, its a generic one, as allen bradley no longer makes these type of devices for devicenet anymore:mad: