Rockwell Automation EDS File Import In Codesys WAGO
Jul 2021
Bulgaria
52
Hello,
These days I am trying to implement a communication via EthernetIP between a PowerFlex 525 drive and a WAGO PFC200 with EthernetIP Scanner.
After a research on the Internet I found out that, for some reason, Rockwell Automation EDS files are not compatible with the CODESYS EDS file structure
When I try to import the EDS file in CODESYS, by the way it is called E!****pit for WAGO but it is based on CODESYS, I got an error.
You can find the error in the attached file.
I imported a FANUC EDS file and it worked fine.
There is this tool EZ-EDS that is used for editing EDS files and some people say that there should not be any arrays or structures in the assemblies of the EDS file. Could this be the reason for this error?
Has anyone got this problem and what would be the procedure to fix this problem?
Best Regards
Konstantin Kolev
I am able to install the EDS files in CODESYS environment, and it does seem possible to configure the PowerFlex. It seems the problem is with the installation process in your specific system. The log you sent shows the text below at the beginning. The screenshot shows the successful installation of the EDS files you sent me in my system.
Wago.Frame.Services.IO.FrameIOException: The file or directory cannot be found. ---> System.IO.DirectoryNotFoundException: The system cannot find the path specified.
Edit: The resolution of the screenshot is not so good, but it shows the EDS having been correctly installed.
I contacted WAGO yesterday and they told me that the EDS file seems to reference another file which is not present. And the reference file is most likely and image file.
I am not sure if I have ever had an image file in the EDS file directory.
Best Regards
Konstantin Kolev
Perhaps, I will try to connect to the PowerFlex 525 drive with the Generic EthernetIP Adapter that is available in the Product Catalog.
I also tried to install all of EDS files simultaneously but I got the same error.
Best Regards
Konstantin Kolev
Can you try installing the CODESYS engineering tool and see if you can add the device. If the CODESYS standard tool allows the installation and configuration of the EDS file as I show, then you can send Wago a complaint about their implementation of the EDS parsing component of their environment.
I noticed in Rockwell AOIs, they add a BOOL Output parameter at the end of the "Parameters" list of each AOI that carries the same name as the...
115
Hello Guys, I am using 1769-L36ERMS PLC by Rockwell which doesn't let me MOV or COP literal text into string datatype? i very well know the...
459
Good Afternoon , Does Rockwell Automation have an Input Card , maybe in the 1734 series , or CompactLogix series that will receive signals...
938
Hi everyone, I'm working on a project that involves using a Keyence LR-X100 sensor in Studio 5000 V35 ladder logic to determine the object's...
723
I have a problem with time sync working in this topology. I have a plc with grandmaster clock controlling motion groups. I wanted to add kinetix...
1,118