S7-300 Event Error

bgtorque

Member
Join Date
Oct 2013
Location
Northampton
Posts
127
Hi All
I'm from an Allen-Bradley background and am having my first experience of Siemens. I have an S7-314 that I keep needing to manually cycle the Run/Stop switch to get it into run. Looking into the diagnostics I get the following error:

1 of 351;
Event ID: 16# 3842
Module OK
Module type: Distributed I/0s
Input address: 2042
Channel information available
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the in the current operating mode
7/15/1994 17:36:13.322

Can anyone guide me where to look to solve this? Thanks,

Ben
 
Exactly, put empty OB blocks mentioned above to PLC - it won't stop but still report the error.
 
The solution for keeping the plc in run is downloading ob82 but you have to look for the fault at your distributet I/O's address 2042. Maybe bad power connections/lov voltage, bad network or faulty hardware..

Jonas
 
OK guys, i've just been back to site and i'm getting the following error: Does this suggest and error with the profiNET connections?
6 of 377;
Event ID: 16# 39CB
PROFINET IO: station Failure
address of the affected station: Input address: 2042
IO system ID: 100
station number: 1
Log. Basic address of the IO controller: 2043
Requested OB: Rack failure OB (OB86)
Priority class: 26
7/17/1994 05:01:22.275
 

Similar Topics

Hey all, first time poster here. I am wondering if anyone has tried using a Keyence SR-X300 barcode scanner to a Micrologix 1400. Keyence sent...
Replies
0
Views
27
Hi Siemens guys! I am experiencing SF fault on our S7-300 (6ES7 315-2AH14-0AB0) CPU from time to time. I've checked the diagnostic buffer and...
Replies
13
Views
170
Have a system that has been running for over a year and all of a sudden getting a ExcessiveVelocityFault on one of the drives when the MSO command...
Replies
2
Views
144
Hello PLCS.Net Forum, First time posting. Let's assume I am a novice. BASIC PROBLEM: My servo/linear piston is no longer zeroed to the...
Replies
9
Views
217
hi... i have an issue in s7 300 plc, while we run the machine(in idle there is no fault) , plc cpu goes in SF mode, after restart the power cycle...
Replies
2
Views
117
Back
Top Bottom