PC Worx Express - While/Repeat Loops
ce_ht
Nov 2017
Derby
Hi, I am currently programming a Phoenix Contact PLC using PC Worx Express. The software and PLC programming in general are still fairly new to me.
I have got the PLC doing what I want it to do by using mainly IF statements but I am having some trouble with loops. I keep getting watchdog errors even when running simple loops, for example I am trying to run the following;
WHILE Global_Reset = FALSE DO
Red_Lamp :=TRUE;
END_WHILE;
I have a number of outputs and counters I want to reset using the global reset input but even with the simple function above I am having no luck.
Thanks for any help
The code should be
IF Global_Reset = FALSE THEN
RED_Lamp := TRUE;
ELSE
RED_Lamp := FALSE;
END_IF
You would use WHILE/FOR loops specifically for repeating a piece code for n no. of times and then EXIT. Your code is stuck in the WHILE loop infinitely and hence you get a watchdog. (You could put an EXIT after RED_Lamp := TRUE and then it would work) but again use a Loop when you really need to. For your specific code above IF THEN ELSE is sufficient.
Hope this helps.
Thanks.
Or you can do it more simple:
RED_Lamp:= NOT Global_Reset ;
There's no need to use IF instruction at all
I have a zip file of a program that I'm told was created in Proworx NxT. Would the comments be stored in it if I could find the software or...
601
I am getting random comm loss (error code 561 i think?) anyway i looked it up and its loss of comm to 2 modules on a controlnet network. The 2...
362
The back story: We have one customer that has some equipment that uses DeviceNet that must remain in place. On those (5) DeviceNet networks they...
908
Working on a site where they are using a DeltaV DCS system. They are using Topworx DVC6200 controllers on their modulating valves. These control...
1,096
When making changes, I was taught to go to Combined > Make Change > go to Offline > will prompt to save > Save > Exit out of program > will prompt...
635