One HMI To Multiple PLC's Best Practice

I am designing the control for a system of processing tanks, each with it's own PLC and controlled by one PC running AdvancedHMI. This is the first system like this I am designing that will consist of a few identical cells and one HMI.

My first thought is to have all the PLC's use the same exact program, just have it's own IP address - something like xxx.xxx.0.1 for tank #1, ...0.2 for tank #2, etc. - but each PLC using the same exact tags and I/O.

I am thinking this would be easier later when adding more tanks (now there is one tank being tested, but depending on demand there will be 4 to 8 tanks eventually)

Should I go with this idea, or have each PLC use different tags so as not to be confusing? I would like to know of any problems or ideas others may have come across doing this.
__________________
Never underestimate the quality of idiots that will be running your machines
http://aabeck.com
  Reply With Quote
Old February 24th, 2018, 08:13 AM   #2
damica1
Member
United States

damica1 is offline
 
Join Date: Aug 2015
Location: Illinois
Posts: 595
What type of PLC? Why does each tank need it's own PLC?

I would probably look at a single PLC + AdvancedHMI + a Modbus TCP controller at each location.

Modbus TCP Controller cost $200.00
PLC $1200.00 - $2500.00

Just a thought!
__________________
David M. Camp

Marshall Electric / https://mei-tech.com/monitor-and-control

Please Download from our download section "Monitor and Control" .pdf.
  Reply With Quote
Old February 24th, 2018, 08:37 AM   #3
Aabeck
Member
United States

Aabeck is offline
 
Aabeck's Avatar
 
Join Date: Feb 2013
Location: Detroit
Posts: 1,060
I will be using ControlLogic PLC's.

Each tank is to be an isolated cell so one can be pulled out for service without interfering with the others and for additional tanks to be added after the first 4 as needed - just controlled by one operator station.
__________________
Never underestimate the quality of idiots that will be running your machines
http://aabeck.com
  Reply With Quote
Old February 24th, 2018, 08:56 AM   #4
lfe
Member
France

lfe is offline
 
Join Date: Jun 2007
Location: Barcelona
Posts: 305
If the PLC's are Modbus TCP capable with Suppanel (an Android app) the thing is as simple as create the Panel for the first tank then clone the panel with a new name, then change the IP in the connection control and voila ! the Panel for the second Tank is working.
  Reply With Quote
Old February 24th, 2018, 09:18 AM   #5
Aabeck
Member
United States

Aabeck is offline
 
Aabeck's Avatar
 
Join Date: Feb 2013
Location: Detroit
Posts: 1,060
Ife,

That basically is what I was planning with Ethernet, clone the panels except for the IP address, and copy and paste HMI screens - I was just wondering if anyone that has done something similar had some problems they encountered.
__________________
Never underestimate the quality of idiots that will be running your machines
http://aabeck.com

Last edited by Aabeck; February 24th, 2018 at 09:40 AM.
  Reply With Quote
Old February 24th, 2018, 09:40 AM   #6
mendonsy
Member
United States

mendonsy is offline
 
mendonsy's Avatar
 
Join Date: Feb 2009
Location: Western NY
Posts: 744
I have done something similar using Omron CP1L PLC's and a Maple Systems touchscreen. The copy and paste screen function isn't quite that simple using that combination because each object on the pasted screen needs to be edited to change which PLC it looks at.
  Reply With Quote
Old February 24th, 2018, 09:44 AM   #7
Aardwizz
Member
United Kingdom

Aardwizz is offline
 
Aardwizz's Avatar
 
Join Date: Dec 2017
Location: Swindon
Posts: 203
I haven't played with Advanced HMI yet, but I've done what you describe using other systems.

If I were doing this in something even as basic as a Panelview, I'd have one replaceable parameter (#1) that I would pass to a screen with the topic name of the PLC as that parameter.Thus all the tags on the screen would be linked as [#1]MyTagxxx.

There'd me a "Master Menu" to pick a "Main Menu" for which Line/(PLC) the user is entering, and that would set the parameter for all screens off the Main Menu.

I know that FTView, iFix, Wonderware all have some method of passing parameters or "substitution tags" or somesuch to a screen so that when a valve object opens a faceplate, there is only one instance of that faceplate, not a zillion.

Surely AdvanceHMI has a similar feature. As I don't know AHMI, so I don't know the mechanics of how tags are linked, so cannot advise you further.

Good luck.
  Reply With Quote
Old February 24th, 2018, 10:04 AM   #8
Aabeck
Member
United States

Aabeck is offline
 
Aabeck's Avatar
 
Join Date: Feb 2013
Location: Detroit
Posts: 1,060
Mendonsy,

In AdvancedHMI each screen has an Ethernet driver (or multiple ones) that all objects look at for it's tag

All I would have to do is change the IP on the driver for each screen, if they end up with 8 tanks I would paste 8 identical screens only having to change the IP address on that screen's driver
__________________
Never underestimate the quality of idiots that will be running your machines
http://aabeck.com
  Reply With Quote
Old February 24th, 2018, 10:25 AM   #9
jstolaruk
Member
United States

jstolaruk is offline
 
Join Date: Dec 2004
Location: Detroit, SouthEast Michigan
Posts: 3,273
Quote:
Originally Posted by Aabeck View Post
Mendonsy,

In AdvancedHMI each screen has an Ethernet driver (or multiple ones) that all objects look at for it's tag

All I would have to do is change the IP on the driver for each screen, if they end up with 8 tanks I would paste 8 identical screens only having to change the IP address on that screen's driver
Should work fine, I do this with the PV+ too.
__________________
"You can live to be a hundred if you give up all the things that make you want to live to be a hundred." Woody Allen
  Reply With Quote
Old February 24th, 2018, 11:46 AM   #10
lostcontrol
Member
New Zealand

lostcontrol is offline
 
lostcontrol's Avatar
 
Join Date: May 2009
Location: NeverSayNever
Posts: 776
You can change the IP address programmatically in AHMI.
That way, develop 1x screen only ��. Much cleaner & more like other system that allow parameters/indirect tags etc.
  Reply With Quote
Old February 24th, 2018, 12:02 PM   #11
Aabeck
Member
United States

Aabeck is offline
 
Aabeck's Avatar
 
Join Date: Feb 2013
Location: Detroit
Posts: 1,060
lostcontrol,

I wasn't aware of that, it sounds like an easier way than the multiple screens I was planning.

I will check into doing that.
__________________
Never underestimate the quality of idiots that will be running your machines
http://aabeck.com
  Reply With Quote
Old February 24th, 2018, 02:35 PM   #12
lostcontrol
Member
New Zealand

lostcontrol is offline
 
lostcontrol's Avatar
 
Join Date: May 2009
Location: NeverSayNever
Posts: 776
There is a technique yo doing so (I think), I’ll have a look & postback when I get a chance.
  Reply With Quote
Old February 24th, 2018, 05:56 PM   #13
Aabeck
Member
United States

Aabeck is offline
 
Aabeck's Avatar
 
Join Date: Feb 2013
Location: Detroit
Posts: 1,060
I dug around the AdvancedHMI forum and found this:

http://advancedhmi.com/forum/index.p....msg759#msg759

The IP address of a driver can be changed after it is stopped.
__________________
Never underestimate the quality of idiots that will be running your machines
http://aabeck.com
  Reply With Quote
Old February 27th, 2018, 05:00 AM   #14
Allen123
Member
China

Allen123 is offline
 
Allen123's Avatar
 
Join Date: Feb 2018
Location: Shenzhen
Posts: 12
Are micro PLCs an option? Micro PLCs with flexible, 'just-enough' control may enable OEMs to differentiate their equipment, particularly in stand-alone machines. By developing a range of stand-alone machines using the same controller platform, OEMs can reduce design time and lower their costs.
__________________
Industrial Panel PC Manufacture at http://www.szjawest.cn/
  Reply With Quote
Old February 27th, 2018, 08:17 AM   #15
Aabeck
Member
United States

Aabeck is offline
 
Aabeck's Avatar
 
Join Date: Feb 2013
Location: Detroit
Posts: 1,060
Allen,

I built a pair of 'sister' machines years ago for an automotive supplier - they were plates on a conveyor that indexed 2" then 3 torque drivers placed screws in to a certain "screw flange to part surface" height.

I built the machines using Crouzet micro-PLC's and they ran fine, even putting out more parts per hour than the customer was asking for and at a better rejection rate than demanded.

BUT - when the customer opened the control panel and saw the 'toys' running them he had major problems. He complained about every aspect of the operation after that and called me back a couple months later, handed me 2 MicroLogic's with 32IO (the machines were running on 10 IO) and demanded I replace the 'toys' and rewrite the program for the ML's. (On the positive side he did pay for the conversion and not demand it be done free)

Maybe if someone made a micro-PLC about the size of a fixed SLC500?
__________________
Never underestimate the quality of idiots that will be running your machines
http://aabeck.com
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Same HMI application for 2 machines - Rockwell HMI & PLC's EICS LIVE PLC Questions And Answers 7 June 14th, 2017 05:00 PM
HMI One App - Multiple Locations; Panelview Plus 7/FTView ME 9.0 dcooper33 LIVE PLC Questions And Answers 12 May 11th, 2017 06:26 PM
Redlion DataStation Plus to Multiple PLCS (Omron) 1 Ethernet Line Tommycai LIVE PLC Questions And Answers 2 September 26th, 2014 10:23 AM
Scan Enet I/O from Multiple PLCs scott.maddox LIVE PLC Questions And Answers 2 August 12th, 2014 07:51 PM
Programming software for multiple AB PLCs manojvivek LIVE PLC Questions And Answers 6 July 9th, 2002 10:10 PM


All times are GMT -5. The time now is 09:11 AM.


.