Recommend Modbus and HART cable

I have a task to connect devices to a Control Logix PLC. First time working Modbus and HART from scratch.

Like to know if I can use the same cable for both the Modbus RTU and HART devices? Looking at Belden 3106A.

Siemens MultiRanger 100 level control. Modbus RTU 2wire multidrop. Eight devices, about 150M from end to end.

Foxboro 875 PH meters. HART 2wire single drop. Max 50M from each device to PLC.

Can I use the same cable for both, or does anyone have a recommendation?

Thanks!
  Reply With Quote
Old March 6th, 2018, 02:57 PM   #2
a062549
Member
China

a062549 is offline
 
Join Date: Feb 2012
Location: Home
Posts: 105
Quote:
Originally Posted by cncsparky View Post
I have a task to connect devices to a Control Logix PLC. First time working Modbus and HART from scratch.

Like to know if I can use the same cable for both the Modbus RTU and HART devices? Looking at Belden 3106A.

Siemens MultiRanger 100 level control. Modbus RTU 2wire multidrop. Eight devices, about 150M from end to end.

Foxboro 875 PH meters. HART 2wire single drop. Max 50M from each device to PLC.

Can I use the same cable for both, or does anyone have a recommendation?

Thanks!
I'd agree that the Belden 3106 is an excellent choice. Correct impedance, with a good jacket for tray application.
  Reply With Quote
Old March 6th, 2018, 06:58 PM   #3
danw
Member
United States

danw is offline
 
danw's Avatar
 
Join Date: Oct 2004
Location: midwest, USA
Posts: 2,834
Near perfect for RS-485:
- third wire for signal ground
- 120 ohm impedance, easy to terminate with common 120 ohm resistors
- super shielding - braid and foil

The shielding and twisted pair will work perfectly for 4-20mA or the transducer-Multiranger connection.

I agree, an excellent choice.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
PLC to HART Gateway, Help Troubleshooting! richleva LIVE PLC Questions And Answers 4 December 18th, 2017 02:37 PM
Modbus Don Diego LIVE PLC Questions And Answers 11 April 19th, 2017 09:35 PM
Hart Network wiring Steve_D LIVE PLC Questions And Answers 2 April 28th, 2016 10:34 PM
How to read Calibration Time remaining from a Hineywell XNX Transmitter using HART sanger LIVE PLC Questions And Answers 4 February 16th, 2014 02:10 PM
Modbus Value scalling Problem suvro2012 LIVE PLC Questions And Answers 9 December 22nd, 2012 11:27 PM


All times are GMT -5. The time now is 06:17 AM.


.