Time-Proportional output for PID on SLC-5/03

I found this question in my Personal Message box ... not sure why the sender didn’t just post it to the open forum ... the questions are valid and pretty common ...



Quote:
Hi Ron

Thank you very much for your explaination about PID....

its seems that u like to help PPL regarding PLC question.

im new on PID....Im using SLC 500 5/03

my question is i wanna control digital OUTPUT to my heater element!(Not Analog output) which bit i should use to Control digital output?

PID

N7:6 = control Block

I:3.4 = process variable(MY thermo couple input)

N7:7 = control variable

my heather element output address is O:2/2
or i will control with internal Bit B3:1/1

pls help me on this question!

if u dont understand the question pls let me know!

thanks ____
Quote:


Greetings ____ ...



first of all, if you follow your original plan and use N7:6 as your control block, then you can NOT use N7:7 as your Control Variable (CV) ... the reason is that the control block requires 23 words of data ... so that means that N7:6 through-and-including N7:28 will be dedicated for use by the PID instruction ... your CV will need to be placed somewhere outside of this range ... let’s use N7:75 just for discussion purposes ...



you said that I:3.4 will be used for your Process Variable (PV) ... maybe - but probably not ... the only way that this will work, is IF (big IF) your thermocouple input module can be configured to give you a signal which is already “scaled-for-PID” ... most modules won’t do this ... the big idea is that the PV signal must range in value from 0 to 16383 ... in most cases this requires the use of some type of “scaling” operation - and a new location for the properly scaled PV signal ... let’s use N7:54 as an example ... use the SCP to do the scaling if your processor will support it ... please tell us what type of input module you’ll be using if you need more detailed help with this ...



now ... to control your digital output, you’ll want to use what we call a “time proportional signal” ... here’s a quick example:








there are different ways of doing it, but this will probably be the best way to demonstrate the basic ideas involved ... experiment with this section of code and if you can’t figure it out, post any specific questions that you might have ... there are a lot of knowledgeable people here on the forum who will be able to help ...



finally ... yours is a good question and one which will benefit a lot of people - so I’ve decided to answer it here on the open forum ... if you have further questions, it would be a good idea to post them here - so that everyone can help each other - and so that we can all learn together ...



I hope this helps ... and welcome to the forum ...
__________________

2-B ?
Best regards, ----+----] [----+------------( )----
Ron | |
PLC Training Boot Camp | 2-B |
+----]/[----+

I once was lost, but now am found, was blind, but now I see.

  Reply With Quote
Old December 10th, 2006, 09:03 PM   #2
ravisashi
Member
Canada

ravisashi is offline
 
Join Date: Oct 2006
Location: montreal
Posts: 8
hi ron thanks for your reply!

what u are trying to say is the TC have to scale b4 its goes to PID?
is that correct?(Max 16383 bit right?) so have to use SCP to scale it and the output of SCP will go to PID PV?

pls correct me if im wrong!

thanks




for your info...i havent got my input module yet!...i planned!
  Reply With Quote
Old December 12th, 2006, 11:51 AM   #3
Ron Beaufort
Lifetime Supporting Member
United States

Ron Beaufort is offline
 
Ron Beaufort's Avatar
 
Join Date: Jul 2002
Location: Charleston, SC
Posts: 4,405
yes ... the PID in the SLC platform is like a blind accountant ... he only (ONLY!) understands 0 to 16383 ... so he regards 0 as his "rock bottom" value ... and he regards 16383 as his "full scale" value ...

now it IS possible (but NOT recommended) to make the PID control a system even when using a faulty/incorrect input scaling range ... but ... the control will not be "optimum" or as "good-as-possible" unless the range is correct ...

hope this helps ... and welcome to the forum ...
__________________

2-B ?
Best regards, ----+----] [----+------------( )----
Ron | |
PLC Training Boot Camp | 2-B |
+----]/[----+

I once was lost, but now am found, was blind, but now I see.

  Reply With Quote
Old December 14th, 2006, 11:54 PM   #4
ravisashi
Member
Canada

ravisashi is offline
 
Join Date: Oct 2006
Location: montreal
Posts: 8
hi ron!...as you said i tried and its work with PID.
at first i had CPU fault....after couple of fine tuning and its works!


Thanks ron!......You are the man!
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Time synchronize between SLC & RSView32 (workstation) for reporting ckchew666 LIVE PLC Questions And Answers 8 April 7th, 2007 03:57 AM
SLC 5/03 passthru to Ch0 DF1 to PV300 BillTo LIVE PLC Questions And Answers 3 August 26th, 2005 05:41 AM
quick panel jr to SLC 5/03 coda9753 LIVE PLC Questions And Answers 0 August 9th, 2005 01:28 PM
SLC 5/03 Fault Steve LIVE PLC Questions And Answers 7 November 21st, 2002 05:59 PM
AB SLC 5/03 real time clock control DRThorne LIVE PLC Questions And Answers 2 August 21st, 2002 11:19 AM


All times are GMT -5. The time now is 01:41 AM.


.