Old July 11th, 2008, 12:53 PM   #1
bierdo
Member
Canada

bierdo is offline
 
Join Date: Jul 2008
Location: Québec
Posts: 2
Difference between a 1747 cp3 and a normal rs-232 cable(scnm9ff)

Hi! I have a new laptop and he doesn't have a COM port. I've tried to communicate with a SLC 5\30 using a 1747-UIC and a RS-232 cable, and it doesn't work... I found that it takes a 1747-CP3 cable to communicate between the 1747-UIC and the SLC... Is someone know how to convert a rs-232 cable into a 1747-cp3 cable? I just need the pinout...
  Reply With Quote
Old July 11th, 2008, 03:33 PM   #2
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 8,473
SLC 5/30? Is this a SLC5/03 or a PLC5/30.
The 1747-CP3 is a null modem cable ( see pic below for pin-out)
To convert a straight thru RS232 cable to a null modem cable you need a null-modem adapter (Radio Shack should have one if needed).
Your 1747-UIC is a USB to DH485 converter. The SLC's port will have to be configured for DH485 protocol for it to work.If you have a SLC5/03 then your 1747-UIC will work with its DH485 port see PDF below for cables. If the SLC's port is configured for DF1 then your going to need a USB to serial adapter.
( the "Keyspan" brand is the best. You can get one at link below.
http://www.plctrainer.net/
Attached Files
File Type: pdf 1747_UIC_Cables.pdf (142.5 KB, 1514 views)
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb

Last edited by Mickey; July 11th, 2008 at 03:41 PM.
  Reply With Quote
Old July 14th, 2008, 07:38 AM   #3
bierdo
Member
Canada

bierdo is offline
 
Join Date: Jul 2008
Location: Québec
Posts: 2
It's a SLC 5/03... I also have a USB to serial (Brand: APC), and if I use this to communicate, which driver will I use in RSLinx?

Last edited by bierdo; July 14th, 2008 at 07:40 AM.
  Reply With Quote
Old July 14th, 2008, 08:02 AM   #4
BillRobinson
Member
Canada

BillRobinson is offline
 
BillRobinson's Avatar
 
Join Date: Oct 2006
Location: Sydney, Nova Scotia
Posts: 185
I would simply use the USB to serial then use DF1 driver to connect the SLC. Be warned though, some USB to serial devices have a limited baud rate. I had a radioshack piece of junk that could only to 9600. I now use a Belkin one and it works on high baud rates.
  Reply With Quote
Old July 14th, 2008, 08:22 PM   #5
panic mode
Member
Canada

panic mode is offline
 
panic mode's Avatar
 
Join Date: May 2003
Location: Toronto, Canada
Posts: 1,962
Quote:
Originally Posted by BillRobinson
...I had a radioshack piece of junk that could only to 9600....
wow, that is low... never seen usb to rs232 adapeter that couldn't do at least 38.4k, usually 115k or better.
  Reply With Quote
Old January 26th, 2011, 08:18 AM   #6
ahad_iiee
Member
Pakistan

ahad_iiee is offline
 
Join Date: Jan 2011
Location: Pakistan
Posts: 1
SLC 5/03 PLC (Processor 1747-L532 C/D) Programming Cable

Hi

I need help,
I need pinout (PC RS232 port) to (PLC Ch0 DB9)
Offline file shows Channel configuration as follows

"Ch0 - DF1 Full Duplex" , "Baud 1200, Parity None",
"Ch01 Driver DH485, Baud 19200",

also need RSLinx communication Procedure.

Pls reply me urgent
  Reply With Quote
Old January 26th, 2011, 09:33 AM   #7
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 8,473
Post # 2 of this thread shows the pin-out but here they are again. Also see links below for procedure and
for other cables in case you don't have a real serial port and need a USB adapter.

http://www.plctrainer.net/ABComSetUp.pdf

http://www.plctrainer.net/PLCProgrammingCables.htm
Attached Files
File Type: pdf 1747-CP3_1756-CP3-PinOut.pdf (31.8 KB, 927 views)
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb

Last edited by Mickey; January 26th, 2011 at 09:35 AM.
  Reply With Quote
Old April 28th, 2011, 12:04 PM   #8
rberry1961
Member
United States

rberry1961 is offline
 
rberry1961's Avatar
 
Join Date: Mar 2009
Location: Merrillville, IN
Posts: 4
The DH 485 cable to use on the 1747-UIC uses a RJ45 connector on each end and is wired straight throug. (i.e. 1-1, 2-2, ... 8-8)
Hope that this helps. It only costs about 2 bucks to make the cable and AB wands $52 for the same thing.
__________________
Ray Berry
Field Service Engineer
  Reply With Quote
Old April 28th, 2011, 12:16 PM   #9
The Plc Kid
Member
United States

The Plc Kid is offline
 
The Plc Kid's Avatar
 
Join Date: Feb 2009
Location: Macon, Georgia
Posts: 3,036
Quote:
Originally Posted by rberry1961 View Post
The DH 485 cable to use on the 1747-UIC uses a RJ45 connector on each end and is wired straight throug. (i.e. 1-1, 2-2, ... 8-8)
Hope that this helps. It only costs about 2 bucks to make the cable and AB wands $52 for the same thing.
Or you can use a pre made ethernet patch cable.
  Reply With Quote
Old July 24th, 2011, 09:57 AM   #10
PLCstarter1884
Member
United States

PLCstarter1884 is offline
 
PLCstarter1884's Avatar
 
Join Date: Jan 2009
Location: Phoenix, AZ
Posts: 18
Question About Serial Cable Pinout

Quote:
Originally Posted by Mickey View Post
SLC 5/30? Is this a SLC5/03 or a PLC5/30.
The 1747-CP3 is a null modem cable ( see pic below for pin-out)
To convert a straight thru RS232 cable to a null modem cable you need a null-modem adapter (Radio Shack should have one if needed).
Your 1747-UIC is a USB to DH485 converter. The SLC's port will have to be configured for DH485 protocol for it to work.If you have a SLC5/03 then your 1747-UIC will work with its DH485 port see PDF below for cables. If the SLC's port is configured for DF1 then your going to need a USB to serial adapter.
( the "Keyspan" brand is the best. You can get one at link below.
http://www.plctrainer.net/
I am trying to connect to a SLC 5/03 via a keyspan usb to serial converter and a homemade cable. I noticed there is a difference in this diagram and the diagram from allen bradley for the serial comm cable http://literature.rockwellautomation...n518_-en-p.pdf

Pin 1 on both connectors in this pinout show a connection. In the Allen Bradley pinout there is no connection. Other pinout drawings as well do not show the connection between 1. Is this pinout listed above incorrect?
  Reply With Quote
Old July 24th, 2011, 11:21 AM   #11
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 8,473
I'm no expert on the handshaking pins. I think both ways will work.

But if you are making your own cable then all you need is pins 2,3 and 5.
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Old July 24th, 2011, 01:16 PM   #12
PLCstarter1884
Member
United States

PLCstarter1884 is offline
 
PLCstarter1884's Avatar
 
Join Date: Jan 2009
Location: Phoenix, AZ
Posts: 18
Quote:
Originally Posted by Mickey View Post
I'm no expert on the handshaking pins. I think both ways will work.

But if you are making your own cable then all you need is pins 2,3 and 5.
Thanks Mickey. I actually got the right pinouts on the cable. 1-1 is not supposed to be terminated on both ends of the cable. I'm using all 8 wires on the connector as setup in the pinout.

What bothers me is that I have the same cable and keyspan converter at work, and I can connect to an SLC 5/05 via DF1 RS232 without any problems. I bought the same keyspan converter and serial cable from work, and downloaded the keyspan driver to be assigned for COM port 5 on my desktop. I have a 5/03 processor at home that I'm trying to connect to now and I keep getting this message in RS Linx "Unable to verify settings due to packet timeout! Check all cables and configuration and try again".

I can easily connect to a micrologix 1000 with a different cable and interface converter and different COM port with RSLink and RSLogix 500.

So I'm pretty sure I have it nailed down with the cable and interface converter. I'm guessing there might be something to configure in the keyspan converter software on my desktop (Keyspan Serial Assistant)? I'll check the settings on the laptop at work tomorrow to try to see what I'm doing wrong here. Thanks!
  Reply With Quote
Old July 24th, 2011, 02:24 PM   #13
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 8,473
This SLC5/03 , does it have a program in it? If so do you have the offline file to check how the ports are configured? The serial port can be configured for DH485,DF1 and ASCII.
If this is just something to learn with then you might condiser defaulting to factory setting. ( DF1 protocol) See proecedure below.
Attached Files
File Type: pdf ClearMemorySLC.pdf (72.3 KB, 315 views)
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Old July 24th, 2011, 03:23 PM   #14
PLCstarter1884
Member
United States

PLCstarter1884 is offline
 
PLCstarter1884's Avatar
 
Join Date: Jan 2009
Location: Phoenix, AZ
Posts: 18
Quote:
Originally Posted by Mickey View Post
This SLC5/03 , does it have a program in it? If so do you have the offline file to check how the ports are configured? The serial port can be configured for DH485,DF1 and ASCII.
If this is just something to learn with then you might condiser defaulting to factory setting. ( DF1 protocol) See proecedure below.
Thanks for your response. That was actually going to be my next question, thinking it was not configured on channel 0 for DF1 protocol. Yes, it's for learning purposes and I don't really need the program that's in there now, but it would of been kinda cool to see! For now, I'll take your recommendation and clear the memory to see if it helps. I'll post back. Thanks Mickey.
  Reply With Quote
Old July 24th, 2011, 04:04 PM   #15
PLCstarter1884
Member
United States

PLCstarter1884 is offline
 
PLCstarter1884's Avatar
 
Join Date: Jan 2009
Location: Phoenix, AZ
Posts: 18
Hey Mickey, thanks for your help. I cleared out the memory and was able to go online. Thanks again!
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -5. The time now is 02:21 AM.


.